    MI- Generator
    Have a note from EE that says all generator control wiresbetween generator and ATS must be run in MI cable and to refer to NEC 700.9. Ican’t find anything specifically that requires these conductors to be run in MIor 2 hour rated.
  2. #2
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,707
    Quote Originally Posted by mstrlucky74 View Post
    In the 2014 edition it's found at 700.10(D)(3) which refers to 700.10(D)(1) (1)-(5).
  3. #3
    Join Date
    Sep 2012
    NJ
    Posts
    1,999
    Thanks, I see. Does RGS conduit give a 1 hour rating. Seems like those conductors between ATS and genset only need 1 hour rating or be run in sprinkler protected area.
    Attached Images Attached Images
  4. #4
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,707
    In general, RGS will not provide any additional fire protection as far as the requirements are concerned, unless it is part of a listed assembly for that purpose.
    By what you sent it looks like you are on the 2008 edition of the NEC. Is this correct?
    It looks like if the control wiring is run entirely in a sprinklered area(s) you would be OK. Depending on the situation and the number of conductors you might have to run, it might actually be cheaper to install sprinklers than comply with any of the other methods listed.
  5. #5
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,164
    Wouldn't this type of building always have sprinklers?
    Rob
  6. #6
    Join Date
    Feb 2003
    New York, 40.7514,-73.9925
    Posts
    4,471
    Are you serving a fire pump? Be sure to consider 695.6
    Ron
  7. #7
    Join Date
    Sep 2012
    NJ
    Posts
    1,999
    Quote Originally Posted by ron View Post
    Yes those POWER conductor are definitely MI cable.
  8. #8
    Join Date
    Sep 2012
    NJ
    Posts
    1,999
    Quote Originally Posted by gadfly56 View Post
    Yes I was referring to 08'.
    Thanks.
  9. #9
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,707
    Quote Originally Posted by infinity View Post
    If you can figure out what class of building and occupancy he has from his OP, you are WAY better at this than I am.
  10. #10
    Join Date
    Sep 2012
    NJ
    Posts
    1,999
    Yes double checked fire protection drawings and entire floor is sprinkler protected.