    Flood lights

    Must outside flood light be installed on a switch, and if so if you could provide the section where the code is located?


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    17,636
    Quote Originally Posted by iragarcia24 View Post
    Must outside flood light be installed on a switch, and if so if you could provide the section where the code is located?


    Sent from my iPhone using Tapatalk
    For residential, there must be some (not necessarily all) switched outside lights at entrances.
    Energy codes, where the state has them, might well prohibit 7x24 lighting. Timer or photocell?
    To do maintenance on fixture, you would turn off the breaker anyway.

  3. #3
    Join Date
    Jun 2017
    Location
    Burkburnett,tx
    Posts
    13
    Quote Originally Posted by GoldDigger View Post
    For residential, there must be some (not necessarily all) switched outside lights at entrances.
    Energy codes, where the state has them, might well prohibit 7x24 lighting. Timer or photocell?
    To do maintenance on fixture, you would turn off the breaker anyway.
    They are photocell lights, some one told me they had to be on a switch within eyesight of the lights


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    17,636
    Quote Originally Posted by iragarcia24 View Post
    They are photocell lights, some one told me they had to be on a switch within eyesight of the lights


    Sent from my iPhone using Tapatalk
    Not in the NEC.

  5. #5
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    11,421
    Quote Originally Posted by iragarcia24 View Post
    They are photocell lights, some one told me they had to be on a switch within eyesight of the lights


    Sent from my iPhone using Tapatalk
    That someone is incorrect. Goldy gave you the requirement, it just involves exterior lights at doors. 210.70(A)(2)(b).
    "Electricity is really just organized lightning." George Carlin


    Derek

  6. #6
    Join Date
    Jun 2017
    Location
    Burkburnett,tx
    Posts
    13
    Thank you all for clarifying!


    Sent from my iPhone using Tapatalk

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •