    Quote Originally Posted by infinity View Post
    I agree, it might be marginally better than this gem that I found in a Post office. Guess that they could get to the earth from the third floor.
    Haven't you ever seen an ECEE (Elevated Concrete Encased Electrode) before. It is also referred in the trade as a Whatfer instead of a Ufer.

  2. #12
    Join Date
    Jul 2006
    Posts
    2,351
    Quote Originally Posted by GoldDigger View Post
    It is also referred in the trade as a Whatfer instead of a Ufer.

  3. #13
    Join Date
    Mar 2007
    Location
    Valdosta, GA
    Posts
    3,734
    Quote Originally Posted by Cow View Post
    Personally, I'd be more concerned about not having a proper ground fault current path and the potential for someone to get shocked, then I would be about ground loops.
    Yeh, that was my explanation to the owner. At that point, cost didn't matter.


    Sent from my iPhone using Tapatalk
    Brought to you by Carl's Jr.

  4. #14
    Join Date
    Mar 2007
    Location
    Valdosta, GA
    Posts
    3,734
    Quote Originally Posted by infinity View Post
    I only wonder why in 2017 people are still specifying IG systems.
    I'm not kidding when I say this is priority number 1 on the electrical installation for these guys. Along with the affidavit, we have to send pictures of ORANGE IG receps to the POS vendor before they will come out to install.

    My supplier ran out of orange receps once, and I used ivory IG receps with the orange IG symbol in the corner. It turned into a crap storm.


    Sent from my iPhone using Tapatalk
    Last edited by Little Bill; 08-10-17 at 12:17 AM. Reason: language
    Brought to you by Carl's Jr.

  5. #15
    Join Date
    Apr 2007
    Location
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    5,884
    Quote Originally Posted by brantmacga View Post
    My supplier ran out of orange receps once, and I used ivory IG receps with the orange IG symbol in the corner. It turned into a crap storm.
    lately, anything with orange on the top of it gets people riled.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~

  6. #16
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,263
    Quote Originally Posted by Fulthrotl View Post
    lately, anything with orange on the top of it gets people riled.
    Careful.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  7. #17
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    3,861
    Quote Originally Posted by infinity View Post
    I agree, it might be marginally better than this gem that I found in a Post office. Guess that they couldn't get to the earth from the third floor.

    Attachment 18208
    I see the problem; fitting instead of a bushing on the EMT... wait, no, they didnt use a rebar to EMT fitting... clamp not listed for use on rebar (ECEE LOL)... I think I'm close... aha, I have it: they used a red wire for ground! That's it! everyone knows you only use red wires on bombs when there is a 50/50 chance of cutting the wrong one with less than two seconds on the timer!!
    Electricians do it until it Hertz!

  8. #18
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,263
    Quote Originally Posted by brantmacga View Post
    I'm not kidding when I say this is priority number 1 on the electrical installation for these guys. Along with the affidavit, we have to send pictures of ORANGE IG receps to the POS vendor before they will come out to install.

    My supplier ran out of orange receps once, and I used ivory IG receps with the orange IG symbol in the corner. It turned into a crap storm.

    This demonstrates the sheer stupidity of people. You require an orange IG receptacle but do not even know enough to check and see if it's actually properly grounded.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  9. #19
    Join Date
    Dec 2011
    Location
    Ocala, Florida, USA
    Posts
    2,232
    I have seen isolated ground requested tons of times. At lease half the time when questioned further, the "specifier" is only envisioning a dedicated ground wire to the nearest panel. I love it when an Electrical Engineer specifies isolated ground and then doesn't provide any isolated ground busses or an additional wire in any of the conduits. I hate it when I have to bid one, because I understand the requirements and I assume there is usually going to be one idiot who doesn't. There was a thread here yesterday that someone was asking about whether to bid to code or spec. Here is one that I will usually just clearly state in my proposal, "Excludes additional wiring or components are required for isolated ground that are not shown on the plans." I will usually highlight it.


    I know what I don't know, and I know where to go to find it!

  10. #20
    Join Date
    Dec 2010
    Posts
    1,215
    Quote Originally Posted by infinity View Post
    I agree, it might be marginally better than this gem that I found in a Post office. Guess that they couldn't get to the earth from the third floor.

    Attachment 18208
    Orange grounding conductor and no grounding bushing?
    The more they overthink the plumbing, the easier it is to stop up the drain