    Quote Originally Posted by Daniel malack View Post
    If you are interpreting the word " isolated " as not being conducted. just stick the ground out side the panel and let it hang in free air! Then it would surely be isolated.

    The confusion is in the what the installer defines as "isolated" .

    If you have an isolated grounding receptacle you attach it to the isolated screw on the receptacle and don't attach it to anything all the way back to main panel ground.
    That would be isolated but it wouldn't be a ground.

    I understand how this stuff works. The confusion comes from the idea that there can be two grounds which are absolutely isolated from each other.

  2. #82
    Join Date
    May 2012
    Location
    Amissville, Virginia USA
    Posts
    150
    Quote Originally Posted by ggunn View Post
    That would be isolated but it wouldn't be a ground.

    I understand how this stuff works. The confusion comes from the idea that there can be two grounds which are absolutely isolated from each other.
    It's real simple. It's isolated for what is going on in the branch circuits. If you isolate the ground at main , other faults won't effect this isolated ground ckt. I believe all isolated ckts are dedicated. You can't isolate it by driving a separate ground rod, uffer, bldg steel, ground ring etc.. you would never get the breaker to trip by running a separate electrode.

    Sent from my SM-T350 using Tapatalk

  3. #83
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    7,957
    deleted

  4. #84
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    20,829
    Quote Originally Posted by Daniel malack View Post
    ... You can't isolate it by driving a separate ground rod, uffer, bldg steel, ground ring etc..
    It is also a violation of 250.50.
    I will have achieved my life's goal if I die with a smile on my face.

  5. #85
    Join Date
    May 2012
    Location
    Amissville, Virginia USA
    Posts
    150
    Quote Originally Posted by Smart $ View Post
    It is also a violation of 250.50.
    Correct. Using a definition of isolated to the extreme would be let it hang outside the panel in free air. Correct isolation is all the way back to the main. If a fault to ground occurs anywhere in the building it won't effect this isolated ckt. Electrons won't back up and go away from source and effect isolated equipment. If you ground every single conduit, box, and fixture. then if a fault to ground occurs it will take path of least resistance, if through sensitive equipment, it will. That is isolated Ground! It is isolated from other effects on the electrical system.

    Sent from my SM-T350 using Tapatalk

  6. #86
    Join Date
    Jun 2015
    Location
    nyc
    Posts
    106
    Quote Originally Posted by Daniel malack View Post
    Correct. Using a definition of isolated to the extreme would be let it hang outside the panel in free air. Correct isolation is all the way back to the main. If a fault to ground occurs anywhere in the building it won't effect this isolated ckt. Electrons won't back up and go away from source and effect isolated equipment. If you ground every single conduit, box, and fixture. then if a fault to ground occurs it will take path of least resistance, if through sensitive equipment, it will. That is isolated Ground! It is isolated from other effects on the electrical system.

    Sent from my SM-T350 using Tapatalk
    in my opinion, the "extreme" solution is to install transformer and connect to it all equipment required IG grounding.

    Sent from my Nexus 5X using Tapatalk

  7. #87
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,044
    Well no. The ground(s) and the secondary side grounded conductor still have to be connected to the the service. You can't have an isolation transformer with the secondary floating.

    There are isolation transformers that are designed to supply "technical power" that have a center tapped secondary. 60-0-60. But the center tap has to be connected to the service ground.

    -Hal