Page 2 of 2 FirstFirst 12
Results 11 to 12 of 12
Thread: residential boat dock
  1. #11
    Join Date
    May 2005
    Tacoma, WA
    Quote Originally Posted by Len View Post
    outside on dock. so i think 6 maybe even 6P i have to find out if dock gets submerged at all
    If the panel will be outside, obviously a NEMA 3R would be the minimum. If it's inside, NEMA 1 is fine. If it's near salt water, I would suggest a stainless steel panel, or put a regular panel WITHIN a fiberglass NEMA 4X Hoffman box.
    In my state (Washington), the code requires "corrosion resistant" enclosures for marina work. Salt air eats up panels REALLY fast.
    Regarding the GFI protection: I would put a 30 mA GFI breaker in the dock panel that feeds the dock power. They aren't cheap, but it is required. You can also put a standard 5 mA GFI breaker, which is much cheaper, but you run the risk of nuisance tripping.
  2. #12
    Join Date
    Aug 2017
    Sussex County, NJ
    Code says that if all branch circuits are protected, main line doesn't require GFI
    2014 Code says that if all branch circuits from shore subpanel are protected, main line doesn't require GFI, 2017
Posting Permissions
  • You may not post replies
  • You may not edit your posts
