Page 1 of 2 12 LastLast
Results 1 to 10 of 12
Thread: residential boat dock
  1. #1
    Join Date
    Oct 2006
    Bucks County
    Posts
    137
    For Florida, what is the requirement for electric for a boat dock for residential. I looked in 2014 NEC and 555 does not apply to residential.
    Specifically i am asking about GFCI protection for feeder and what type of panel would i need, like NEMA 3r or 6P?
    Thanks for your responses.
  2. #2
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,048
    The 2017 NEC puts resi boat docks back under article 555, where they were prior to the 2002 NEC.
    "Electricity is really just organized lightning." George Carlin
    Derek
  3. #3
    Join Date
    Oct 2006
    Bucks County
    Posts
    137
    thank you. i just read the 2017.
    i do have an issue. it says gfi protection required on mains, feeders and branch. if you put gfi on feeder and you put another in sub panel they trip. you cannot put 2 in line i believe this is a typo.
  4. #4
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,536
    Quote Originally Posted by Len View Post
    Yes, GFCI and/or GFP/GFCI devices can be in series. But also note, terms are important here. The 2017 requires 30 ma GFP on the supply to a marina, not GFCI.
    Also, does this even apply in Florida for a residential dock? I thought Florida was on the 2014 NEC.
  5. #5
    Join Date
    Oct 2006
    Bucks County
    Posts
    137
    they are but chief inspector says because it is in 2017 it implies intent and they will follow.
  6. #6
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,704
    Quote Originally Posted by texie View Post
    If 2014 applies they can't make you do it, but would not be a violation to install that 30mA GFP on the feeder either.
  7. #7
    Join Date
    Oct 2006
    Bucks County
    Posts
    137
    if inspector wants it he gets it. not worth arguing this. i would put gfp on feeder to dock. I do not see anything about what type of panel should be used. NEMA rating i am referring to
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,704
    What conditions is the panel likely subject to? If it is indoors and not likely to get wet NEMA 1 enclosure is fine, outdoors will likely need at least 3R, but if water will spray/splash from below may need to be more then 3R.
    Salt water - may need to add an X to the designation.
  9. #9
    Join Date
    Oct 2006
    Bucks County
    Posts
    137
    outside on dock. so i think 6 maybe even 6P i have to find out if dock gets submerged at all
    thanks
  10. #10
    Join Date
    Jan 2009
    Posts
    14,048
    That does not sound kosher(enforceable).
    Derek
Posting Permissions
  • You may not post replies