    Quote Originally Posted by JJWalecka View Post
    A single gang masonry box is installed in a kick plate of a stairwell...it is sitting back and 1-3/4 or there of...I need being the box out flush with block. Thinking a handy box extension ring might work.
    On a non-flammable surface, you are allowed 1/4" setback, and if you've more than that, the plastic ring I linked will bring it up to code.

    Here's a 1 7/8" handy box extension:

    http://www.homedepot.com/p/RACO-Sing...-665/202783891
    Electricians do it until it Hertz!

  2. #12
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    975
    Quote Originally Posted by JFletcher View Post
    On a non-flammable surface, you are allowed 1/4" setback, and if you've more than that, the plastic ring I linked will bring it up to code.

    Here's a 1 7/8" handy box extension:

    http://www.homedepot.com/p/RACO-Sing...-665/202783891
    I thought it's 1/8".

  3. #13
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    4,244
    Quote Originally Posted by Coppersmith View Post
    I thought it's 1/8".
    See 314.20. You are allowed 1/4" setback when the wall surface isnt flammable.

    314.21 says the gap around the box can only be 1/8".
    Electricians do it until it Hertz!

  4. #14
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    975
    I stand corrected. Thanks.