Page 2 of 2 FirstFirst 12
Results 11 to 14 of 14
Thread: Masonry extension ring
  1. #11
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    Quote Originally Posted by JJWalecka View Post
    A single gang masonry box is installed in a kick plate of a stairwell...it is sitting back and 1-3/4 or there of...I need being the box out flush with block. Thinking a handy box extension ring might work.
    On a non-flammable surface, you are allowed 1/4" setback, and if you've more than that, the plastic ring I linked will bring it up to code.
    Here's a 1 7/8" handy box extension:
    http://www.homedepot.com/p/RACO-Sing...-665/202783891
    Electricians do it until it Hertz!
  2. #12
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    1,553
    Quote Originally Posted by JFletcher View Post
    I thought it's 1/8".
  3. #13
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    Quote Originally Posted by Coppersmith View Post
    See 314.20. You are allowed 1/4" setback when the wall surface isnt flammable.
    314.21 says the gap around the box can only be 1/8".
  4. #14
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    1,553
    I stand corrected. Thanks.
    Sent from my SCH-I535 using Tapatalk
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts