Page 1 of 2 12 LastLast
Results 1 to 10 of 11
Thread: Stainless Panel required on a Salt water boat dock
  1. #1
    Join Date
    Jul 2017
    Clearwater, Florida, USA
    Posts
    2
    Hi
    We have a concrete fixed pier which has several boat docks attached over a salt water Bay. We've installed a standard watertight panel with branches to each dock, water tight fixtures, etc. The panel is more than 30 inches above high water level. The inspector (as AHJ) is requiring a Stainless enclosure around the panel to protect from salt water in the air, saying the panel will rust in under 2 years and is not appropriate for the location.
    Has anyone else heard of this being required? Thank you for the advice.
  2. #2
    Join Date
    Jun 2012
    NW Ohio
    Posts
    985
    Probably good advice.
    Looking at the service from a vacation home that was built about 4-5 years ago on the beach has a regular 3R enclosure that has disintegrated.
  3. #3
    Join Date
    Jul 2015
    Wilmington, NC USA
    Posts
    282
    If this is a requirement, how did it get through plan review?
    I've installed and see installed SQ D I-line panels with the marine paint option. It's an epoxy paint that does a pretty good job of keeping the panels from rusting.
    I am not aware of an NEC requirement for this to be SS, but I do agree it is a good idea. I wonder if the AHJ would accept a professional coating on the panel?
    How big of a panel are we talking about?
  4. #4
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,727
    Quote Originally Posted by KMR View Post
    Hi
    It certainly isn't explicit in the NEC. He may be within his rights to require the additional protection under the "suitable for the intended use" principal. It would be better if the local jurisdiction codified that requirement, however. You may have to start investigating the wonderful (and very expensive) world of Hoffman enclosures.
  5. #5
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,172
    Quote Originally Posted by gadfly56 View Post
    I believe it is explicit enough in Sections 110.11 and 300.6. The NEC is NOT a design manual for the inexperienced [Section 90.1(the very first NEC rule)]
    I was on the Working Committee for IEEE P1713, Recommended Practice for Electrical Shore-to-Ship Connections. There are quite a few conditions that should be considered for marine installations.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.
  6. #6
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,524
    Quote Originally Posted by rbalex View Post
    ....The NEC is NOT a design manual for the inexperienced [Section 90.1(the very first NEC rule)
    (Sigh) If only that were true today.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,755
    Hi
    He is right in that you need to protect from corrosion, he is wrong in that stainless is the only option unless there is some local requirement. PVC or fiberglass enclosures certainly won't rust out.
  8. #8
    Join Date
    Aug 2013
    New York, NY
    Posts
    473
    Hi
    NEC required or not, it's an exceptionally good idea. Anything that's not 316 stainless or non-metallic will ROT in the weather in a marine environment. Quickly. I'm dealing with this right now: a fellow subcontractor did not properly weatherproof some of their equipment for use in a marine environment. It stopped working electrically, and started showing rust within two weeks of installation. Our (properly weatherproofed) gear, in 316SS and fiberglass enclosures, is working fine.
    Salt air and spray will very shortly destroy non-rated equipment. 3R isn't gonna cut it.
    SceneryDriver
  9. #9
    Join Date
    Jul 2017
    Posts
    2
    Thank you
    Dear All, Thank you for weighing in on the problem. The advice to Marine Coat it or use some other kind of panel is good. I will check if the AHJ actually does have a local code requirement too.
    Kind regards, KMR
  10. #10
    Join Date
    Apr 2007
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,539
    Quote Originally Posted by SceneryDriver View Post
    my experience has been, that hot dipped galvanized steel is pretty
    resistant to salt spray corrosion. honestly, better that 316. that info
    was given to me by an old shipbuilder, who did restoration work on old
    sailboats. he had to change out a couple hot dipped gal nails in the hull,
    and they'd been in salt water for about 80 years at that point.
    if there is anywhere the coating is broken, it's gonna rust in a week. toast in two years.
    i put some 3R panels near the water 4 years ago. as in within 30' of the salty pacific.
    if i get a chance, i'll stop by and take some photos. i'm over in that area tomorrow afternoon.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~
Posting Permissions