    We have a large multi-family mixed use building we are just now bringing out of the ground. We're trying to figure out a solution to the over-sized conductors on too-small lugs. All of our residential units require only a 100Amp loadcenter. We've solved the connection at that end of the feeder by buying 150A rated MLO loadcenters which have lugs good for up to 300KcMIL. However, it's the other end that has me concerned. The meter/main meter packs we're using are Eaton (Cutler-Hammer) and the 2-pole mains will be BR2100 circuit breakers. Submittal sheets say the maximum wire size on their lugs is 1/0. However, due to distances, we have about half the building requiring #2/0 feeders, plus a small handful of them at both #4/0 and #250KcMIL. I've been researching ways to reduce the conductor size to fit on the 1/0 lugs but not finding anything conclusive. Am curious to know what others have done as inevitably, there are others who have run into this before us. I can't find any manufacturers who make a compression reducer that will go from 250 to 1/0. Mechanical lugs are plentiful for this. I'm hoping I can find out from others what they've done in the past. Also curious about code quotation to back us up with the inspector for having 10' of 1/0 AL at the beginning of a #250 AL feeder in case they have a problem with it.
  2. #2
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,285
    There is no code quotation to back up your plan because the code is permissive. It does not list exhaustively all the things that are allowed.
    You are using larger conductors to limit voltage drop. Do the voltage drop calculation adding 10' of smaller, but code approved, wire at the end and notice that the difference is negligible.
    Doing what you suggest is a separate junction box will also avoid any bending space problems with the larger wire.
  3. #3
    Join Date
    Dec 2013
    Eugene, OR, USA
    Posts
    11
    Quote Originally Posted by GoldDigger View Post
    Thank you! My thinking was inline with what you suggested... the voltage drop difference will be negligible and easily demonstrated for the inspector (a former employee!!). Was hoping I wasn't missing anything and appreciate the comment. We had already determined to have an oversized wireway above the meter paks and will most likely do the reducing splices there.
    Thank you.
  4. #4
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    Quote Originally Posted by StevenLeuck View Post
    Use a Polaris connector that goes from the 4/0-250MCM to a smaller jumper wire that will fit the 1/0 lugs:
    http://www.polarisconnectors.com/pdfs/nsi/it_series.pdf
    Using a few feet of 1/0 from that connector in a gutter below/above the meter will not affect voltage drop but a fraction of a %.
    eta: as far as code issues, as long as the 1/0 is suitable for the calculated ampacity and OCPD, you will be fine. A few might want torque values or % fill of your gutter/panel/can housing.
    seta: If you're on a 150A breaker, you'll have to use 1/0 in copper only; AL is good for just 120A.
  5. #5
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    Also, you realize that if you use Polaris connectors on both ends and 90*C wire, you are permitted to use the 90*C table for ampacity for the wire between the 2 (but 75*C for the wire from connector to meter and breaker). I know you oversized for VD reasons, just throwing that out there.
  6. #6
    Join Date
    Apr 2007
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,583
    you can buy finger lugs that hypress onto aluminum wire, and have a smaller extrusion to fit under the lug. the good thing is that they provide a permanant connection for aluminum that does not deteriorate over time, nor loosen. they are the only way i will land aluminum conductors onto a breaker. it leads to a connection as good as copper.
    in severely corrosive situations, you can use panduit heat shrink that will give you a permanant waterproof connection. works in a salt air environment.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~
  7. #7
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,363
    Reducing wire size is common when you're using much larger conductors for voltage drop. Here's several hundred feet of parallel conductors for a 200 amp ATS.
    Rob
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,101
    Quote Originally Posted by Fulthrotl View Post
    One problem he likely runs into though is that there is not enough bending space for a 250 conductor in a meter center compartment that is only rated for 100-125 amps.
  9. #9
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,101
    Quote Originally Posted by JFletcher View Post
    My understanding is there is 150 amp main lug panel (which will accept his 250 conductors), but the feeder breaker is only a 100 amp breaker and only accepts up to 2/0 conductor. The conductor is larger for voltage drop reasons and not ampacity reasons. Is also likely there isn't appropriate bending space on the supply end even with a reducing device that attaches directly to the conductor.
  10. #10
    Join Date
    Jan 2007
    Posts
    3,531
    Quote Originally Posted by infinity View Post
    That picture is extremely deceiving to say the least.