    Whats the reason for the neutral? Wouldn't a simple bi-metal switch work just as well?
    Attached Images Attached Images  

  2. #2
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    4,252
    Line/load markings? I see that overload as just making/breaking one conductor, not hot and neutral with a ground wire.
    Electricians do it until it Hertz!

  3. #3
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,836
    If that is for a single phase motor, depending on the way the motor was wound, one lead would protect the running winding and one would protect the starting winding and the third would be the common.
    If Billy Idol or John Denver is on your play list go and reevaluate your life.

  4. #4
    Join Date
    Nov 2009
    Location
    Opelousas, Louisiana
    Posts
    532
    There is a heater inside the thermal overload which creates enough heat to cause the overload to trip if the overload is surrounded by insulation.

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,942
    Sounds like a recessed lighting thermal to me. Are the conductors in the photo are black, white and blue?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,749
    Quote Originally Posted by Mgraw View Post
    There is a heater inside the thermal overload which creates enough heat to cause the overload to trip if the overload is surrounded by insulation.

  7. #7
    Quote Originally Posted by Mgraw View Post
    There is a heater inside the thermal overload which creates enough heat to cause the overload to trip if the overload is surrounded by insulation.
    Well that explains why the neutral is there, but are you saying the ambient air, when reaching a setpoint, causes the heater to come on thus tripping the overload or

    that the heater is on all the time and when the ambient air temp is added the overload then trips?

    Still don't understand why a simple switch wouldn't do the same thing

  8. #8
    Join Date
    Nov 2009
    Location
    Opelousas, Louisiana
    Posts
    532
    They are used to prevent insulation being wrapped around non ic rated cans. The heater is always on.

  9. #9
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    9,453
    Quote Originally Posted by Mgraw View Post
    The heater is always on.
    All the while we look for ways to save every milliwatt of electricity.....
    Cheers and Stay Safe,

    Marky the Sparky

  10. #10
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,836
    I gotta get my eyes checked. I did not see the word "can" in the title of this thread the first time I looked at it.
    If Billy Idol or John Denver is on your play list go and reevaluate your life.