This Chiller say it has a minimum circuit ampacity of 485amps. Is this what number I use to size my conductors? Or do I have to take the 485 amps at 125% to size my conductors. I am not sure if when the manufacture marks a minimum circuit ampacity that they took the load at 125% to come up with there 485 amps.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You only need to use the 485 amps to size the conductors. The manufacturer has done all of the calculations for you. :cool:
 