    I'm not sure if I should add all the ohms of the resistors together and divide by the voltage which would be 50÷50 equals 1 or divide the voltage by the 10 which would be 50÷10 = 5 honestly not 100% sure this is why am trying to get help with this problem
  2. #22
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,704
    Quote Originally Posted by sclement View Post
    Ohm's law: E=IxR
    You have determined you have 50 volts and total circuit resistance of 50 ohms. 50V / 50 Ohms = 1 Amp.
    Now figure how much voltage is across the 10 ohm resistor if it has 1 amp flowing through it.
    Did that help?
  3. #23
    Join Date
    Oct 2014
    Utah
    Posts
    13
    Quote Originally Posted by kwired View Post
    Ohm's law: E=IxR
    Did that help?
    10×1 = 10 so 10 volts! Thanks for the assistance I really appreciate it all
  4. #24
    Join Date
    Oct 2014
    Utah
    Posts
    13
    Voltage Drop
    thanks to all the folks that have been helping with the different problems I've posted! here's another one that's got me scratching my head
    Single phase 120 V, 16 amp single phase load is connected to a12 AWG THHN conductor. The equipment name plate requires no more than a 3% voltage drop on the branch. What is the maximum wire length from the panel where the voltage drop will not exceed 3% (k=12.9)
  5. #25
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,704
    Write out your VD calculation - fill in the known values, you will have to calculate what 3% is before filling that in. You should have all components of the formula except length - reorganize the equation to solve for that missing value.
    I want you to try this before it gets shown to you.
  6. #26
    Join Date
    Mar 2017
    US
    Posts
    11
    Transpose equations
    [QUOTE=sclement;1851686]thanks to all the folks that have been helping with the different problems I've posted! here's another one that's got me scratching my head
    Single phase 120 V, 16 amp single phase load is connected to a12 AWG THHN conductor. The equipment name plate requires no more than a 3% voltage drop on the branch. What is the maximum wire length from the panel where the voltage drop will not exceed 3% (k=12.9)[/Qequipm
    The questions you are asking are generally the same questions in which you are trying to find (×) write this formula on a piece of paper. Cma=2×k×i×l÷vd. I expained to you what the letters represented in the last question. With this formula you can answer all the questions asking for (l)length,(cma) circular mil or the wire size, vd, or (i)amp. Which ever variable they are looking for needs to be isolated by itself using the the formula. Transposing is important to know because this skill will be needed in basic ohms law questions. Hope this helps.
  7. #27
    Join Date
    Oct 2014
    Utah
    Posts
    13
    Here is my attempt I know something is out of order, and I'm not sure when to apply the 3% in the equation.
    2 x 12.9 x 16 = 412.8
    412.8÷6530=0.063215926
  8. #28
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    You are missing Vd and Cmil in your equation
    Vd = Nominal voltage × voltage drop percentage
    Vd = 120V × 3%
    'Plug' this Vd into the equation as a known value.
    Cmil = 2 × K × I × L ÷ Vd
    I will have achieved my life's goal if I die with a smile on my face.
  9. #29
    Join Date
    Oct 2014
    Utah
    Posts
    13
    Vd = 120V × 3%
    I had circular Mills in there the 6530 and length is unknown I'm just not sure when to apply the 3% Factor and how to come up with length? Thanks!!
  10. #30
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Yeh. You did as a second step. Learn to do it all in one step.
    In the equation I wrote, take all knowns to one side of the equal sign; change preceding operator sign when you do: multiplication to division, division to multiplication.
    Cmil ÷ 2 ÷ K ÷ I × Vd = L