    Bonding and Grounding of UPS

    I am looking for information on the N-G bondingrequirements for UPS when on battery? Do you have to have N-G bondingjumper in battery mode? What is the latest NEC2017 requirements. Thank you.

  2. #2
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,353
    The NEC just says to provide a N-G bond if it is a separately derived service (SDS).

    It depends on the UPS design and the associated bypass to figure out if it is a SDS.

    For example, look at pages 12- at https://www.vertivco.com/globalasset...ion-manual.pdf
    which is an older Liebert UPS with diagrams.
    Ron

  3. #3
    Join Date
    May 2003
    Location
    Leesburg, VA
    Posts
    7,052
    As noted above it depends on the UPS, if you have a bypass with a neutral from the source then you would not bond the neutral on the output, if you have true isolation with a SDS on the output you bond the neutral.

    This does not change if you are n battery or not.
    Brian John
    Leesburg, VA