    LNG and Chemical plants are largely Groups C & D. Occasionally, we see a small patch of Gp B (Hydrogen), but the question I have is: are there any significant differences in conduit sealing requirements for Groups A & B locations vs C & D in either Divisions 1 or 2?
  2. #2
    Join Date
    Feb 2003
    Illinois
    Posts
    23,355
    No difference in the requirement for the locations of seals, but not all seals are listed for Groups A and B. Same applies to other fittings used in Class I, Division 1, Group A & B locations.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  3. #3
    Join Date
    Apr 2016
    Georgia
    Posts
    271
    Quote Originally Posted by don_resqcapt19 View Post
    Thanks for the input.