Thread: 501.10(B)(4), 501.15(B)(1) - Class I Division 2 conduit seals entering enclosures
  1. #1
    Join Date
    Apr 2016
    Georgia
    Posts
    454
    Just want to be completely sure on this one:
    A switch (or other arcing device), installed in Class I Division 2 location, with factory sealed or hermetically sealed contact block, does NOT require an explosion proof enclosure and therefore, does not require a conduit seal....
  2. #2
    Join Date
    Dec 2010
    Posts
    1,381
    Correct.
    The more they overthink the plumbing, the easier it is to stop up the drain
  3. #3
    Join Date
    Apr 2016
    Georgia
    Posts
    454
    Quote Originally Posted by dkidd View Post
    Correct.
    Thanks
  4. #4
    Join Date
    Dec 2010
    Posts
    1,381
    Attached Images Attached Images
  5. #5
    Join Date
    Apr 2016
    Georgia
    Posts
    454
    Thanks -
    EDS series is also good for Division 1. I was looking at Allen-Bradley, Bulletin 800G Pushbuttons, with non-metallic housing for Division 2 applications.
  6. #6
    Join Date
    Feb 2003
    Illinois
    Posts
    23,577
    For Class I, Division 2 applications, I use the 800H operators with the sealed contact blocks (800T-XAP) in the Rosite enclosures.