    Bonding permanently installed swimming pools AKA above ground swimming pools

    We have recently installed electrical systems for a few above ground swimming pools. We are coming across some that have 4-#8 bare copper ground pigtails for meeting the bonding requirements. In this case, can we use split bolts to bond the 4 points of the pool or must we use irreversible crimps?

  2. #2
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,472
    You can use split bolts.

    680.26(B)
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  3. #3
    Join Date
    Dec 2010
    Location
    Tennessee NEC:2008
    Posts
    4,127
    If we can't use split bolts I'm in trouble a 1000 times over!
    If you aim at nothing, you will hit it every time!

  4. #4
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    873
    May have to check if your split bolts are listed for direct burial if it is the case in your situation having them buried.