    Hello everyone,
    We are installing a new 120/208v 3800A service in a commercial building. There are no drawings or specs to go off of, more of a design build job.
    The switchgear is made up of 3 sections of busbar, one service disconnect switch and two distribution panels.
    We are using two of the sections of gear to land our wire. Each section will have 8 parallel feeds of 500kcmil copper conductors which makes 16 conductors per phase. So essentially 2, 3800A feeds from two utility vaults. One vault to one section, the second vault to another.
    I am being told that we need to bring 2 GECs to the water pipe and 2 supplemental GECs to building steel (a set for each section).
    My question is, since the sections share the same bus, A B C N and G, do we need to do this or could we just bring one GEC to the main water pipe and one supplemental GEC to building steel?
    Any help is appreciated, thank you.
  2. #2
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,163
    The GEC's will go to the single service disconnect, one for each electrode if you run two separate GEC's. #3/0 copper is the largest required for the water pipe or building steel.
    Rob
  3. #3
    Join Date
    Aug 2017
    New York
    Posts
    2
    Great, thank you.
  4. #4
    Join Date
    Jun 2017
    WI, USA
    Posts
    297
    Quote Originally Posted by sparky315 View Post
    Am I reading this correctly: one of the service feeders lands on busbar in a distribution section?
  5. #5
    Join Date
    Aug 2004
    Northern illinois
    Posts
    15,755
    The only way this makes sense to me is that the bus bar sections are just there as a place to land the wires from the utility. They then feed the disconnect switch which feeds the distribution panels. I don't know why you need 16 500 KCM wires though for a 3800 amp service.
    Bob
  6. #6
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    18,599
    Can you elaborate on that? Same POCO transformer? Paralleled service feed?
  7. #7
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by petersonra View Post
    Still, doesn't make sense. 8 sets of 500's are only good for 3040A (double-ended supply) and 16 sets are absolute overkill for a 3800A service.
    I will have achieved my life's goal if I die with a smile on my face.
  8. #8
    Join Date
    Aug 2004
    Northern illinois
    Posts
    15,755
    Even if it is Aluminum 16 sets seems like Overkill
    Bob
  9. #9
    Join Date
    Aug 2004
    Northern illinois
    Posts
    15,755
    10 sets of copper 500 kcm would make sense for a 3800 Amp service.
    It would kind of make sense that they picked an odd service size to make do with the most economical wire solution but 16 sets just does not make any sense to me at all.
    Bob
  10. #10
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Aluminum and voltage drop?