Thread: Compression Splices

  1. #1
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    1,671

    Compression Splices

    Most of the time spec calls for mechanical splices but have to use compression in this case. Do compression take longer than mechanical and is so why? Any particular compression splice you guys favor? Thanks.

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,794
    We use Burndy with battery operated crimpers. Yes they take a little longer because you need to crimp both sides of the splice (anywhere from 2-5 per side) and then install a cold shrink. A Polaris type splice you just strip, insert, and torque. Done.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    1,671
    Quote Originally Posted by infinity View Post
    We use Burndy with battery operated crimpers. Yes they take a little longer because you need to crimp both sides of the splice (anywhere from 2-5 per side) and then install a cold shrink. A Polaris type splice you just strip, insert, and torque. Done.
    Thanks. Why cold shrink and not heat shrink? Only familiar with heat shrink.

  4. #4
    Join Date
    Feb 2003
    Location
    New Jersey
    Posts
    3,387
    Not sure what you're crimping but I use these for electric services :

    https://commerce.ilsco.com/e2wShoppi...197:3100012379

    If you have $$ to burn like Infinity does you can use a $600 - $700 Greenlee battery operated power crimper or you can get one of these for about $150:

    https://www.delcity.net/store/V!Crim...-Tool/p_800107

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,794
    Quote Originally Posted by mstrlucky74 View Post
    Thanks. Why cold shrink and not heat shrink? Only familiar with heat shrink.
    Cold shrinks require no tools and are somewhat more foolproof. In over 30 years I have never used heat shrinks on compression splices.




    Quote Originally Posted by goldstar View Post
    Not sure what you're crimping but I use these for electric services :

    https://commerce.ilsco.com/e2wShoppi...197:3100012379

    If you have $$ to burn like Infinity does you can use a $600 - $700 Greenlee battery operated power crimper or you can get one of these for about $150:

    https://www.delcity.net/store/V!Crim...-Tool/p_800107
    At Mrluckys labor rate two journeymen using that battery crimper for two or three days will pay for itself over a manual crimper.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Feb 2003
    Location
    New Jersey
    Posts
    3,387
    Quote Originally Posted by infinity View Post
    At Mrluckys labor rate two journeymen using that battery crimper for two or three days will pay for itself over a manual crimper.
    If you're planning on making a lot of crimps maybe you're right. While I'd love to have one of those power crimpers the job would have to justify the cost.

  7. #7
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,794
    Quote Originally Posted by goldstar View Post
    If you're planning on making a lot of crimps maybe you're right. While I'd love to have one of those power crimpers the job would have to justify the cost.
    I agree completely, for a few crimps on an occasional service the manual ones are fine but for any type of large work, big riser boxes or services, etc. the battery ones are the way to go. Would hate to do this by hand.

    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  8. #8
    Join Date
    Feb 2003
    Location
    New Jersey
    Posts
    3,387
    I agree. Nice work BTW !!! I've already had carpal tunnel surgery and my fingers occasionally lock up just from squeezing pliers for so many years.

  9. #9
    Join Date
    Apr 2007
    Location
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,147
    Quote Originally Posted by infinity View Post
    Cold shrinks require no tools and are somewhat more foolproof. In over 30 years I have never used heat shrinks on compression splices.






    At Mrluckys labor rate two journeymen using that battery crimper for two or three days will pay for itself over a manual crimper.
    yeah, it will.

    the cold shrinks are faster by far
    than heat shrinks, but far more expensive.

    i've used the panduit heavy walled heat shrinks
    a lot. it's UL listed for direct burial @600 volts.
    the panduit stuff is in 3' and 4' lengths. you cut
    to fit.

    it's 10%~20% of the cost of 3m cold shrinks.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~

  10. #10
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    1,671
    Quote Originally Posted by infinity View Post
    Cold shrinks require no tools and are somewhat more foolproof. In over 30 years I have never used heat shrinks on compression splices.






    At Mrluckys labor rate two journeymen using that battery crimper for two or three days will pay for itself over a manual crimper.
    No tools? How is it done?