300kva tranny with 200A 208V secondary

Status
Not open for further replies.

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Customer wants to use an existing 300kva 480V primary to feed a new 208y/120 200A PNL.
How can I determine the min size OCPD and conductor size for the primary to handle inrush?
Is this even compliant?
Thanks
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
To get 200A out at 208V I could feed the primary with 100A at 480V. A 300kve tranny I would normally feed with 500MCM and a 400A OCPD.

Wondering if the 100A breaker would handle the inrush.
 

under8ed

Senior Member
I believe that since the transformer is much larger than required, you would like to provide it with as small as a feed as possible.There would be a problem with inrush if you only feed this with enough current to provide the 200 amps for the panel. I have used transformers larger than required, and have run up against inrush keeping them from powering up when feeding with less than about half of normal line current. This was using time delay fuses also, if using other protection, you may not even be able to go that low.
There are other issues with using such an over sized transformer, ours were temporary solutions opposed to a permanent installation.
 