  1. #11
    Join Date
    Jul 2005
    Posts
    744
    Quote Originally Posted by jumper View Post
    Guess I am a hack then.

    Join the crowd...

  2. #12
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    15,513
    Quote Originally Posted by cdslotz View Post
    I bet a dollar to a donut that those specs allow MC only in furred walls and fixture whips, ....just a guess
    The tags on those circuits show 3/4"C ......do you just ignore that?
    The dwg also clearly shows running two separate conduits yet the consensus seems to be that requirement should be ignored in favor of running just one. And why does it need to be #12? Maybe you could get by with #14. How far are we willing to go on cheating on the requirements in the specs and the dwgs?
    Bob

  3. #13
    Join Date
    Jul 2005
    Posts
    744
    Quote Originally Posted by petersonra View Post
    The dwg also clearly shows running two separate conduits yet the consensus seems to be that requirement should be ignored in favor of running just one. And why does it need to be #12? Maybe you could get by with #14. How far are we willing to go on cheating on the requirements in the specs and the dwgs?
    Because the tags say #12...what is the point to this statement?

    mrlucky74 already stated they were coming from the same panel, according to the schedules

  4. #14
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    1,532
    Quote Originally Posted by cdslotz View Post
    I bet a dollar to a donut that those specs allow MC only in furred walls and fixture whips, ....just a guess
    The tags on those circuits show 3/4"C ......do you just ignore that?
    It also leads me to believe there is a 3/4" minimum spec....

    Just as an in-house company policy, we do not run MC home runs, and we use a hard pipe main trunk for MWBC's with J-boxes and drops to furred walls and up to fixture whips

    MC cable is allowed above hung ceilings.
    We don't run MC homeruns either. I'm talking about pipe from panel to a box close by then MC 150' to another box by the equipment then conduit to the equipment.

  5. #15
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    1,532
    Quote Originally Posted by cdslotz View Post
    Because running MC 150' in a commercial building is hack imo...probably is against the spec too...
    Why would it be against the spec to run MC above a hung ceiling....whether 50' or 200'?

  6. #16
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    15,513
    Quote Originally Posted by cdslotz View Post
    Because the tags say #12...what is the point to this statement?

    mrlucky74 already stated they were coming from the same panel, according to the schedules
    because if you are going to ignore one thing on the dwgs for your own convenience why can't you ignore anything you don't want to do, especially if it still meets code.
    Bob

  7. #17
    Join Date
    Jul 2005
    Posts
    744
    Quote Originally Posted by petersonra View Post
    because if you are going to ignore one thing on the dwgs for your own convenience why can't you ignore anything you don't want to do, especially if it still meets code.
    What was I ignoring? I was complying.....

  8. #18
    Join Date
    Jul 2005
    Posts
    744
    Quote Originally Posted by mstrlucky74 View Post
    Why would it be against the spec to run MC above a hung ceiling....whether 50' or 200'?
    If your spec allows MC above the ceiling...no problem.
    I was merely guessing...based on the tags on your drawing...EMT is required....jeezus

  9. #19
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    15,513
    Quote Originally Posted by cdslotz View Post
    What was I ignoring? I was complying.....
    I was referring to the idea of running only one conduit instead of the two shown on the drawing.
    Bob

  10. #20
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,424
    Quote Originally Posted by petersonra View Post
    The dwg also clearly shows running two separate conduits yet the consensus seems to be that requirement should be ignored in favor of running just one. And why does it need to be #12? Maybe you could get by with #14. How far are we willing to go on cheating on the requirements in the specs and the dwgs?
    #12 is the minimum conductor size in mrluckys jurisdiction.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted