Results 1 to 6 of 6
Thread: 65 amps
  1. #1
    Join Date
    Jan 2016
    Fresno Ca
    Posts
    150
    65 amps
    The plans call for a 65 amp over backfeed breaker, existing 200 amp de rate main to 175, which only leaves room for 65 amp, I can't find a 65 amp breaker can I go up to the next standard size 70 amp but then I'm over the 120% thanks
  2. #2
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    9,597
    Quote Originally Posted by SAP View Post
    Who drew up those plans? There is no 65A breaker.
    If you are under the 2014 NEC, you use 125% of the nameplate inverter current, not the breaker rating, to make your 120% rule calculation.
  3. #3
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,320
    Quote Originally Posted by ggunn View Post
    So the 120% rule doesn't use the panel buss rating anymore.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  4. #4
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    9,597
    Quote Originally Posted by Dennis Alwon View Post
    705.12(D)(2)(3); case (b) is the 120% rule. The main breaker rating plus 125% of the inverter nameplate current cannot exceed 120% of the bus rating. It's the backfed breaker rating that no longer applies.
  5. #5
    Join Date
    Jan 2016
    Fresno Ca
    Posts
    150
    So I have two 6000 solar edge single phase inverters 25 amps 1.25 percent of each inverter is 31.25, backfeed going to main would be 62.5. If I'm reading right I can put whatever breaker in my main which in this case would be a 70 amp thank you
  6. #6
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    9,597
    You can put in any breaker you want as long as it adequately protects the conductors between it and the inverter AC combiner. Qualify the bus in the AC combiner under 705.12(D)(2)(3)(c).