Page 1 of 2 12 LastLast
Results 1 to 10 of 11
Thread: Bonding of the main panel
  1. #1
    I have been having a conversation with the local power company over bonding the neutral and the ground in the main breaker panel of a residence.
    The power company is requiring us to bond the neutral and the ground in the meter base attached to the house. By doing this, should the main breaker panel be treated as a sub-panel and the neutral bus and ground bus be isolated?
    The power companies argument is, by having the main breaker panel neutral and ground bonded it is creating a parallel path to ground. I tend to agree with them on this issue.
  2. #2
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    18,765
    The NEC allows for multiple bond points in the region between the meter and the service disconnect under some circumstances.
    Or, as long as you provide a raceway or wire EGC separate from the POCO neutral, you can separate EGC and neutral in the panel.
  3. #3
    GoldDigger, could you please tell me what section of the NEC you are referencing?
  4. #4
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    3,777
    Quote Originally Posted by midamericairon View Post
    What exactly do you mean by this? The Neutral is factory bonded to the cabinet in a meter enclosure. Do they want you to bring your GEC into the meter socket?
    A few things to note: The NEC doesnt specifically prohibit "a parallel path" at the service (it does use the term for separately derived systems, see 250.30(A)(1) Ex #2). 250.6 discusses "objectionable current" but it is not clear what objectionable current is.
    One final thing: Note in the above I was discussing current flowing on raceways. You said "parallel path to ground " which is different if that is literally what you meant. The NEC does not require a single point earthing system. One could have multiple GEC's connected at different points or auxiliary electrodes (see 250.54).
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,704
    POCO's bond the neutral to everything and is a little surprising they mentioned anything here.
    According to NEC the meter (in most typical self contained metering applications) is still a part of the service conductors and all grounding/bonding ahead of the service disconnecting means is done to the grounded conductor (neutral in most cases). NEC also requires a bonding jumper at the service disconnecting means and separate grounded and equipment grounding conductors beyond that point.
  6. #6
    Join Date
    Feb 2003
    Minnesota
    Posts
    6,672
    You haven't said where the Service Disconnect is located. Is it inside the "main breaker panel", as you call it? Or is it part of the meter, or separate from both the meter and the "main breaker panel"?
    Another Al in Minnesota
  7. #7
    Join Date
    Feb 2003
    Fl
    Posts
    16,872
    That is a typical installation here in the southeast.
    No, the separation takes place after the service disconnect.
    Sounds like your POCO has a good understanding of the way things work, be thankful, many don't.
    Roger
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,704
    As mentioned neutral is usually already bonded to the cabinet in a meter socket, and even in combination meter/mains/loadcenters.
    They only thing that may need to be done is connect to a grounding electrode - though most POCO will already have a rod at any structure they provided.
  9. #9
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by roger View Post
    +1
    A parallel grounded [neutral] conductor pathway on noncurrent-carrying metal parts on the POCO-side of the main disconnecting means has long been considered as permitted and not objectionable current. Those that feel it is install nonmetallic raceway between enclosures. I've not seen nor heard of any AHJ that requires it, though.
    FWIW, the main bonding jumper is always located in the main disconnecting means enclosure(s) regardless of being bonded elsewhere on the POCO side. Bonding elsewhere on the consumer side is, in almost all cases, a Code violation.
    I will have achieved my life's goal if I die with a smile on my face.
  10. #10
    Join Date
    Sep 2017
    geneva
    Posts
    5
    I believe you can bond neutral to ground at following location
    1. Service conductors
    2. Meter panel
    3. At the service disconnect
    Mike has Video on this on YT.
Posting Permissions
  • You may not post replies
  • You may not edit your posts