User Tag List
Page 3 of 6 FirstFirst 1 2 3 4 5 ... LastLast
Results 21 to 30 of 53
Thread: Definition of Feeder
  1. #21
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,394
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    Yes but the proposal has an exception when there is an overcurrent protective device in between the load center and a piece of equipment only then I want that normally called feeder to be called a branch circuit. Thus the entire run between a panel and a single piece of equipment is a branch circuit whether there is a disconnect with overcurrent protective device in it or not
    what is the benefit of doing so?
    Bob
  2. #22
    Join Date
    Mar 2008
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    10,478
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by al hildenbrand View Post
    The conductors coming to the work bench SSU, when fused, are Feeder conductors. The conductors between the fuse LOAD side terminal and the Outlet are the Branch Circuit. The SSU is the "final OCPD."
    I can go along with that.
    Cheers and Stay Safe,
    Marky the Sparky
  3. #23
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,364
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    I believe here is the issue. 430.62 speaks of feeder for fixed motor load(s). This states that a feeder should be based on the largest overcurrent protective device for a motor plus the sum of other motors. We have only one motor so a 3 phase 20 hp motor @ 208 volts is 59.4 amps. Table 430.52 tells us to take 250% of the load for a polyphase inverse time breaker-- 148.5 amps
    This means the feeder technically should be 148.5 amps instead of a conductor size for the branch circuit at 125% 74.25 amps
    430.62 Rating or Setting — Motor Load.
    (A) Specific Load. A feeder supplying a specific fixed motor
    load(s) and consisting of conductor sizes based on 430.24 shall
    be provided with a protective device having a rating or setting
    not greater than the largest rating or setting of the branch circuit
    short-circuit and ground-fault protective device for any
    motor supplied by the feeder [based on the maximum permitted
    value for the specific type of a protective device in accordance
    with 430.52, or 440.22(A) for hermetic refrigerant motorcompressors],
    plus the sum of the full-load currents of the
    other motors of the group
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  4. #24
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,364
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Maybe article 430.62 should be changed????
  5. #25
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,394
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    430.62 only allows you to increase the size of the feeder OCPD above what the ampacity of the feeder conductors might otherwise limit you to. It is not the minimum rating of the feeder OCPD.
    Bob
  6. #26
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,364
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    I believe it is--- read it again it states the max size of the short circuit , ground fault protective device
  7. #27
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,394
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It does not seem to say what you think it says. "Not greater than" means a maximum upper limit is set, but it does not affect how low the rating can go.
    All the "maximum permitted value" language does is allow you to apply the maximum allowed rating to the calculation as opposed to the rating of the actual OCPD used. It does not set a floor, but a ceiling.
    Bob
  8. #28
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,364
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    The examples on test materials say exactly what I think it says
  9. #29
    Join Date
    Feb 2003
    Minnesota
    Posts
    7,071
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    430.62 regulates "Part V. Motor Feeder Short-Circuit and Ground-Fault Protection."
    430.62 directs you to 430.24 to size the conductors. That's in Part II.
    Another Al in Minnesota
  10. #30
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,364
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    If the wire between the panel and the disconnect is a feeder then that wire must be sized to the overcurrent protective device....NO? The branch circuit is sized per the motor
Posting Permissions
  • You may not post replies
  • You may not edit your posts