    First, lets re-look at the words in 430.62:
    430.62 Rating or Setting — Motor Load.
    (A) Specific Load.
    A feeder supplying a specific fixed motor load(s) and consisting of conductor sizes based on 430.24 shall be provided with a protective device having a rating or setting not greater than the largest rating or setting of the branch circuit short-circuit and ground-fault protective device for any motor supplied by the feeder [based on the maximum permitted value for the specific type of a protective device in accordance with 430.52, or 440.22(A) for hermetic refrigerant motor compressors], plus the sum of the full-load currents of the other motors of the group.
    The rule is a SHALL BE. So, it is "required". WHAT is required? ? ? The OCPD rating or setting NOT BE GREATER THAN. The rule does NOT say BE EQUAL TO, only "not be greater than". With this in mind, let's revisit your example from earlier:

    Quote Originally Posted by Dennis Alwon View Post
    I believe here is the issue. 430.62 speaks of feeder for fixed motor load(s). This states that a feeder should be based on the largest overcurrent protective device for a motor plus the sum of other motors. We have only one motor so a 3 phase 20 hp motor @ 208 volts is 59.4 amps. Table 430.52 tells us to take 250% of the load for a polyphase inverse time breaker-- 148.5 amps

    This means the feeder technically should be 148.5 amps instead of a conductor size for the branch circuit at 125% 74.25 amps
    For that 3 phase 20 hp motor @ 208 V, is the OCPD "next size" of 80 Amps "not greater than" 430.52's 148.5 Amps? ? ? Yes.

    Or, the OCPD could be 90, 100, 110, 125, etc. as all are "not greater than". The actual OCPD chosen is a design choice. All that the language of 430.62 does is prevent the OCPD rating or setting from going ABOVE your example's 148.5 Amps.

    Your argument that the cost of the largest OCPD is too great isn't a SAFETY issue, is it? Isn't the CMP primarily interested in safety only?
    Another Al in Minnesota

  2. #52
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,346
    Well, we will see what they say as I had already sent in the second re-wording. I am tired of it- the whole thinking is that the entire run is really a branch circuit and IMO, to call it otherwise feels wrong. There are differences so.... I realize this isn't a major change but I thought it worthwhile. The only reason, IMO that the cmp doesn't want to change this is that it complicates things
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #53
    Join Date
    Sep 2017
    Location
    Claverack, NY, USA
    Posts
    15
    Another way one could look at this is that a feeder usually (but not always) terminates in a load center or panelboard where the downstream wiring becomes branch circuits. If the wiring provides power to more than one load (multiple motors for example), it could be considered a feeder even if it originates in a panel of some type. I am all for clarifying things that are ambiguous but I have seen clarifications that generate more confusion than they solve.