    Owner is out of town and doesn't want to deal with motor until he comes back. I'm just hoping he's not going to try and blame me for the new motor burning up. (We don't know if it did yet.) I'll take a little blame, but seems to me the engineer for thing should have specified heaters, and the original installer should have known it needed heaters. If the thing was properly overcurrent protected in the first place, I would not have even been there. On the plus side, I now know a lot more about motor protection.
  2. #42
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,755
    Quote Originally Posted by Coppersmith View Post
    Most general purpose single phase motors already have integral overload protection. This one being designed specifically for pumps (from what I recall) however likely needs additional overload protection.
  3. #43
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    Quote Originally Posted by kwired View Post
    You must have outrageous utility bills, I figured 7.5 hp even if only 80% efficiency would only cost me maybe around 70 cents an hour to run.
    I get roughly the same as you. Maybe he meant $30 a day and lives in an area where electricity is 20-30c/kw-hr
  4. #44
    Join Date
    Jul 2006
    Posts
    7,736
    To this point, it's also possible that this is not the original motor, and the original one DID have integral thermal protection, so the original circuit design was legit. Then when it went bad (again, probably because someone opened a valve and repeatedly overloaded it), nobody noticed that the replacement motor did NOT have integral thermal protection and needed a different circuit. It's hard to know the complete history of something like this if you were not there from the beginning.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  5. #45
    Join Date
    Jun 2010
    Posts
    1,928
    Do you guys not have an ammeter?
    If it's drawing much more than the name plate, then you stop there.
    You'll have an idea if it's dragging if you run it dry briefly and observe or listen how it slows down.
  6. #46
    Join Date
    Sep 2008
    UK
    Posts
    11,373
    Quote Originally Posted by Electric-Light View Post
    Jraef mentioned measuring the current in post #3 and, of course, it's the obvious thing to do.
  7. #47
    Join Date
    Mar 2014
    South Florida
    Posts
    217
    Too late to measure the current
    Any update on this? I'm interested to know the result.
    You shouldn't take the blame for lack of motor thermal protection, unless you designed the electrical system. Trying a 70 amp breaker to get the thing running wasn't a great idea and you may have to answer for that. The electrical designer should take blame for misrepresenting the work scope (failure to identify code required equipment) and redesign to provide motor thermal protection. Either way, you should absolutely get paid if you have to supply and install a motor controller.
    If an EE designed the motor feeder circuit, they should have made sure overload protection was provided, either integral to the motor or external. If they didn't know this they shouldn't be consulting, imo.
  8. #48
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    1,486
    Quote Originally Posted by drktmplr12 View Post
    I agree. I'm waiting for the client to call me back to work on it (and kinda hoping he never does.)
  9. #49
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,755
    My answer to that is Square D's motor calculators recommend an 80 amp breaker for a 7.5 HP single phase motor, and that NEC allows up to 100 amp before it must fail to start on that before you can upsize it even more.
  10. #50
    Join Date
    Mar 2014
    South Florida
    Posts
    217
    I can see that argument being made, except the calculator (slide card, right?) states that 80A thermal mag is for short circuit protection only and depends on an enclosed starter with overload heaters for thermal protection. Taken without this context, that argument can work. However, it would be cherry picking information.