    Here is the data plate for a motor I hooked up. (It powers a waterfall feature in an artificial mountain behind a large residence. Gotta love rich people.) I'm told it's the same size motor as one that burned up. The existing breaker was a 2-pole 40 amp @ 240v. The wiring is #6 THHN/THWN. The motor tripped the breaker after about 15 seconds. (Tried several times.) I looked up the calculations and if I am correct it should be a 70 amp breaker. Note that the data plate says "31 amps" and not "31 FLA". I assumed they were the same thing. I installed the 70, the motor ran about 2 minutes and then started to smoke. I flipped off the breaker. The breaker was very warm and the handle was squishy. After the breaker cooled for a few minutes, it appeared to operate with it's normal feel. There is no motor starter or heaters in the circuit.
    1) Is 70 amps correct?
    2) Why would the breaker handle get squishy? It's a SqD QO.
    3) Is there an electrical issue here (beside the breaker size)? I personally think the flow is obstructed causing excessive motor loading. I suggested to the owner he call the plumber back (who installed the motor) to check for obstructions.
    4) I also suggested that if there is no obstruction, a call to a motor repair specialist would be in order to check the motor for proper operation. Was this a good call?
    5) Should there be a DOL motor starter with heaters in the circuit or it it OK without heaters?
    Attached Images Attached Images
  2. #2
    Join Date
    Jul 2013
    Renton, WA
    Posts
    758
    Load is too big for 7.5 HP.
    re: check for obstructions or the valve is too FAR open, increased flow at constant head (waterfall) = higher load. Need to look at the pump flow vs. power curve vs. head curve. Plumber did not set things up correctly for 7.5 HP.
    The statement: After the breaker cooled for a few minutes, it appeared to operate with it's normal feel is ambiguous - as is ran for a few minutes OK? or ran for a few hours OK? or ran fine with valve partially closed? or ran with ho head?, etc.....
    What is the desired flow and how high is the 'waterfall'.
  3. #3
    Join Date
    Jul 2006
    Posts
    7,322
    Quote Originally Posted by Coppersmith View Post
    No, not if there is no starter with overloads in the circuit. In fact if that's the case, even the 40A is not legal. Running overload protection must be maximum of 125%, no "next size up". 125% of 31A is 38.75A, a 40A breaker is not legal for this purpose per 430.32. 70A is so far off it's not even funny, but if you DO install a motor starter with OL heaters, then 70A works. I assume you determined 70A by virtue of 430.52, but that only counts AFTER you have satisfied 430.32
    Squishy? You mean the breaker seems like it will trip easily? That could be that the breaker has tripped so many times now that it is wearing out.
    If flow is obstructed in a centrifugal pump, the current would DROP. Flow = work performed, work performed = power. Less flow, less power.
    It's more likely that the pump was improperly sized for the desired flow and you are over loading it as a result. In other words someone may have sized it for a particular head (height) and pipe size, then when the fountain was built, the head height was lower and/or the pipe was larger, so there is MORE flow than the pump is rated for, leading to the motor overloading and since there is no starter w/ OL heaters, only the breaker takes it off line eventually. It's also possible that someone installed a throttling valve knowing that the pump flow needed modulation, then someone later opened that valve further because they wanted more flow, not understanding the effect this would have on the pump.
    Absolutely. If that motor were the type that had internal thermal trips, it is REQUIRED to state that on the nameplate, which it does not. So when it does not say that, you must provide it externally.
    So in conclusion:
    1) You MUST add a motor starter with thermal protection set for 31A
    2) most likely I'm willing to be that it will trip, because something in your fountain design is wrong and the pump is overloading due to excessive flow. You will either need to add a throttling valve and use a clamp-on ammeter to adjust the flow to where the motor current is 31A or less, or get a larger motor.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  4. #4
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,212
    The spec information is here. It looks like it shouldn't have heaters, it's direct on line start.
    We'd need the pump specs, but in any event, you can't overload the motor if the head is too low. The pump output will vary as the sum of the static and velocity head, but it won't overload unless you grab the impeller and lock it. Something else must be at work here. Even if you dead head the pump, if it's centrifugal, it will simply churn the water in the case. You can heat the water to boiling this way, but it would take more than two minutes. Has anyone checked to see if there is excessive runout, offset, or angular misalignment?
  5. #5
    Join Date
    Jul 2006
    Posts
    7,322
    Quote Originally Posted by gadfly56 View Post
    Being DOL start has nothing to do with needing OL protection or not. The "heater" in that spec sheet is referring to a motor space heater, i.e. to keep condensation out of it. The part of the spec where you can tell it needs OVERLOAD protection (aka "heaters") is where it says
    Thermal Device - Winding None
    That means, per 430.32, YOU must supply external motor running overload protection.
  6. #6
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,134
    A motor has to have heaters, either internal or on a starter. This one has to start across the line because it's single phase and you can't soft start it.
    If the pump is moving more water than the motor can handle then the motor will pull high amps. It needs some back pressure to work right.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.
  7. #7
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    1,160
    Quote Originally Posted by Jraef View Post
    OK, squishy wasn't a very exact word. Normally, a slight push of a breaker handle in the off direction would cause it turn off with a "snap". When I pressed on the handle it didn't snap, it resisted my pushing, felt spongy, and finally turned off when I pressed very hard. For a moment, i thought it was going to be locked-on and I would be in deep doodoo.
    I was suggesting that the obstruction was on the output side of the pump. I'm no expert, but it seems to me that if the pump was attempting to push a column of water and it wasn't succeeding this would slow the impeller which would raise the current draw.
    So in conclusion:
    I'll relay this to the owner and suggest he have the design checked. I'll also inform him a starter with heaters must be installed. Thanks.
  8. #8
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    1,160
    I'll give these details to the owner. Thanks.
  9. #9
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    18,765
    A centrifugal pump spins the water to that "centrifugal force" slings the water out the output fitting. If no water moves, no water is being accelerated and no energy is transferred into the water (except for a small amount of friction.)
    Same thing happens with an impeller. Only a positive displacement pump will take more power as head increases (as long as the same volume of water moves) because the piston is moving water the same distance against a higher pressure.
    It does not matter whether you restrict the input or the output, the physics of the moving (or not moving) water is the same. Water is not compressible.
    You can see this effect with a vacuum cleaner. If you block the input or the output the motor speeds up.
  10. #10
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,212
    Quote Originally Posted by ActionDave View Post
    This does not make physical sense. The pump will operate along the pump curve, and the output will be inversely proportional to the total head loss. The motor is never going to spin faster than 1,750 RPM. Think of it this way, if I had a tank 3 feet deep filled to the brim, and I set up the suction at 1 foot above the bottom of the tank and set up the discharge back into the tank at the same elevation, am I going to burn out the pump?
    If I dead head the pump causing it to churn, the impeller only "slips" past the water. It doesn't draw more and more current in that case either.