    Parallel Conduit Runs & Wire

    So NECA Manual Of Labor Units gives recommended labor unit discounts for parallel conduit runs. They also give the discounts for the wire run in the parallel runs. So there is a savings in pulling wire in parallel runs? Do you agree there is a time saving in the wire pulling as well? This have to do with reel setup? Thanks.

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,424
    They're likely assuming that there will be a labor savings because the pulls are in the same physical locations on both ends and you won't need to move your equipment very far to go from pull to pull. Other than that you're still pulling the same amount of conductors through the raceways.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Apr 2016
    Location
    Tampa, Fl
    Posts
    129
    Quote Originally Posted by mstrlucky74 View Post
    So NECA Manual Of Labor Units gives recommended labor unit discounts for parallel conduit runs. They also give the discounts for the wire run in the parallel runs. So there is a savings in pulling wire in parallel runs? Do you agree there is a time saving in the wire pulling as well? This have to do with reel setup? Thanks.
    Absolutely, Since NECA labor units are only 50% actual installation labor, the other 50% is in material layout, set-up , etc. When you pull in parallel conductors much of the 50% of the lay-out, material procurement and set-up is already completed with the 1st of the parallel runs.