balconies

Status
Not open for further replies.

north star

Senior Member
Location
inside Area 51
+ & + & +


"Hendrix asked:
balconies -
All balconies now require receptacles, but do they require lighting?"
It depends !.......This is a Residential or [ Commercial ] Building Code
question..........Which codes & edition are applicable to your question ?




+ & + & +
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
No, and receptacle only required if the balcony is accessible from the floor on which it resides. Or a stairway leads to it from exterior:roll:
 

tom baker

First Chief Moderator
Staff member
No, and receptacle only required if the balcony is accessible from the floor on which it resides. Or a stairway leads to it from exterior:roll:

If its a Juliette balcony, it still requires a receptacle.

210.53 (3) Balconies, Decks, and Porches. Balconies, decks, and
porches that are attached to the dwelling unit and are accessible
from inside the dwelling unit shall have at least
one receptacle outlet accessible from the balcony, deck, or
porch. The receptacle outlet shall not be located more than
2.0 m (61?2 ft) above the balcony, deck, or porch walking
surface
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The NEC does not require lighting outlet at a balcony for a residence. It only requires lighting outlets at every entrance or exit that has grade level access. 210.70(A)(2)(b)
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
If its a Juliette balcony, it still requires a receptacle.

210.53 (3) Balconies, Decks, and Porches. Balconies, decks, and
porches that are attached to the dwelling unit and are accessible
from inside the dwelling unit shall have at least
one receptacle outlet accessible from the balcony, deck, or
porch. The receptacle outlet shall not be located more than
2.0 m (61?2 ft) above the balcony, deck, or porch walking
surface

Yeh, in a nut shell that's what I said thanks for the code article.
 

electricalist

Senior Member
Location
dallas tx
Rich people want the strangest things.
Seriously we did some high end custom houses and what they had were from the street view it was built out on the front 2nd floor.looks like a semi balcony with a window and you could actually open the window and step out onto it. It had an mini rail.
I know there are plugs there and it seems like we had to.
 
Status
Not open for further replies.
Top