    Hammond power has found me a Y075PKCN3L0U (LINK) in stock.
    It looks like what i need but i was unsure of whether or not I'd want to order the 'Neutral Kit' for it?
    I've attached the schematics for the system that this transformer would be powering (just the 480VAC portion)
    _XFMR help.pdf
    the Hammond Power rep that I'm talking to is not really willing to give me any guidance...
  2. #32
    Join Date
    Apr 2006
    Springfield, MA, USA
    Posts
    3,160
    The Y075PKCN3L0U doesn't get connected to the neutral, and your load doesn't require a neutral.
    You bring three phases 480V plus egc (PE in your drawing) to this transformer, and three phases 600V plus egc to your load.
    -Jon
  3. #33
    Join Date
    Dec 2016
    pittsburgh, pa
    Posts
    61
    Quote Originally Posted by winnie View Post
    -Jon
    thank you!, just wanted to verify...
    are there typically lugs in these big transformers for the EGC's to land?
  4. #34
    Join Date
    Nov 2007
    Posts
    844
    Quote Originally Posted by emiller233 View Post
    IMO, 75kVA is not that big. I think the 480V side lines will be no more than #AWG 2, iirc.
  5. #35
    Join Date
    Feb 2012
    United States
    Posts
    605
    Typical egc lugs? Yes.