ground fault on Optional Standby and on Equipment branch in Hospitals

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
I'm aware of 700 and 701 allowing us not to provide GF. What about Equipment branch (in hospitals) and Optional Standby in non-hospitals?
 

Maders

Member
Location
Boston, MA
I'm aware of 700 and 701 allowing us not to provide GF. What about Equipment branch (in hospitals) and Optional Standby in non-hospitals?

517.17(B) prohibits additional levels of ground-fault protection from being installed on the load side of an essential electrical system transfer switch. The equipment branch is part of the essential electrical system per 517.30(B)(1). I am not aware on any prohibitions on the installation of ground-fault protection on article 702 optional stand-by systems. Hope this helps Mike.
 