Thread: 480 to 600 Transformer help - for testing a system

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Join Date
    Dec 2016
    Location
    pittsburgh, pa
    Posts
    50

    480 to 600 Transformer help - for testing a system

    We have a system that we will need to test to pass a SPE-1000 certification thru Intertek.

    This system will operate in Canada or in the USA, so it is designed to run on both: 600VAC, 3-phase as well as 480. There is a 75KVA transformer (Delta to Wye) on the machine to drop the voltage down to 480VAC when in Canada. So if the system is in the USA, they will not use the transformer and wire it to 480.

    My question is for the SPE-100 testing we need to run this thing at 600VAC to pass the inspection.

    Can we use our shops 480V and run it thru a 480V to 600V step up 75KVA transformer (just for during the inspection)? Would this need to be another delta-WYE transformer? What about the grounding?

    i attached a picture of the current transformer wiring (600V to 480V)
    Click image for larger version. 

Name:	xfmr.jpg 
Views:	268 
Size:	8.6 KB 
ID:	18443

  2. #2
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,317
    You can use your shop's 480V and run it thru a 480V to 600V step up 75KVA transformer. If you could get a Delta Wye (where 480V is the Delta and 600V is the Wye) and bond the X0 of the Wye to the Ground (separately derived service), then feed 3 phase conductors and an equipment grounding conductor to the equipment's step down transformer.
    Ron

  3. #3
    Join Date
    Dec 2016
    Location
    pittsburgh, pa
    Posts
    50
    Quote Originally Posted by ron View Post
    You can use your shop's 480V and run it thru a 480V to 600V step up 75KVA transformer. If you could get a Delta Wye (where 480V is the Delta and 600V is the Wye) and bond the X0 of the Wye to the Ground (separately derived service), then feed 3 phase conductors and an equipment grounding conductor to the equipment's step down transformer.

    PERFECT! thanks for the help and the quick reply also!

  4. #4
    Join Date
    Feb 2012
    Location
    United States
    Posts
    577
    If it was me, I would NOT waste the extra money on the D-Y xfmr since I already will be using the one in the machine!

    I would simply buy a 3ph 480/600 volt auto xfmr.

    75kva is d-y about $ 6000.00, but auto about $ 3000.00.

    Depending where u r, if in canada, Rex xfmr is good place, if in us midwest, controlled magnetics, mi. Or equiv.

    Sent from my SM-G900V using Tapatalk

  5. #5
    Join Date
    Dec 2016
    Location
    pittsburgh, pa
    Posts
    50
    Quote Originally Posted by mike_kilroy View Post
    If it was me, I would NOT waste the extra money on the D-Y xfmr since I already will be using the one in the machine!

    I would simply buy a 3ph 480/600 volt auto xfmr.

    75kva is d-y about $ 6000.00, but auto about $ 3000.00.

    Depending where u r, if in canada, Rex xfmr is good place, if in us midwest, controlled magnetics, mi. Or equiv.

    Sent from my SM-G900V using Tapatalk
    I've never used an auto transformer, or even know much about them. Quick Google search says it's just a single core transformer with multiple taps one both like e &load side. Is that accurate?

    Are there any other pros/cons to using one of these?

    Do you just ground the chassis of the auto transformer to the shop supply and the system this is powering up?

    I've got quotes back for a d-y transformer, and they are pretty long lead times. So I am looking for any alternative that I could possibly get faster. Cheaper and smaller is always good! So I'm liking the sounds of this auto transformer

    I'm am in the USA (Pennsylvania), so I don't know if I could use your supplier. I will certainly check into it tho!

  6. #6
    Join Date
    Feb 2012
    Location
    United States
    Posts
    577
    Quote Originally Posted by emiller233 View Post
    1) I've never used an auto transformer, or even know much about them. Quick Google search says it's just a single core transformer with multiple taps one both like e &load side. Is that accurate?

    2) Are there any other pros/cons to using one of these?

    3) Do you just ground the chassis of the auto transformer to the shop supply and the system this is powering up?

    4) I've got quotes back for a d-y transformer, and they are pretty long lead times. So I am looking for any alternative that I could possibly get faster. Cheaper and smaller is always good! So I'm liking the sounds of this auto transformer

    5) I'm am in the USA (Pennsylvania), so I don't know if I could use your supplier. I will certainly check into it tho!
    1) "just a single core thng" is a pretty bad description. Most transformers have a "single core" for each phase so that is no unique description for autoxfmr... multiple taps is good sttatement though. Yes, each phase is wound around single core just like an isolation 9iso) xfmr. And just like a typical iso xfmr primary winding, it has "multiple taps." The auto xfmr just stops there: it does not have a secondary winding. Finished. Done. That's all folks. Just a primary winding. So yes, a single winding [per phase] with taps. In your case at 480v and at 600v. Looks just like an iso xfmr. Reason it is cheaper it is just the pri winding, no cost for a secondary winding, and its physical size is reduce to (1-480/600)*75= 15kva physical size; hence you are paying for basically a 15kva xfmr instead of a 75kva.

    2) pros and cons? sure some potential ones already mentioned by other replies. But none of these re likely to effect you at all. Consider: your 75kva xfmr probably has Z (impedance) of about 5%. An auto xfmr has much lower Z than an equi iso, so you may be adding 2% more with it in series. Unless your machine uses some unique requirement servos such as Siemens, that require <3% Z input, this added 2% certainly won't bother it. Especially for just a single test. Sure it is a Y configuration, but like an induction motor, whether it is Y or D config, it has no meaning to you - it is simply going to be used as a voltage change device. Either will do the job as well and as transparently to you and your machine.

    3) No ground required or used; sure you can ground the metal "core" - there is likely a ground terminal on it for you.

    4) Suggest you ask them what they have in stock that can do your job; often they have something. As xfmr supplier, we often can get something required if needed quick so you should be able to - if you ask.

    5) Both places I posted ship worldwide. Many many others do too.

  7. #7
    Join Date
    Apr 2006
    Location
    Springfield, MA, USA
    Posts
    2,969
    An 'autotranformer' is one where there is a single coil (note: single for a phase) with multiple taps for your input and output voltages, rather than separate primary and secondary coils.

    A single phase transformer with separate primary and secondary coils can be connected as an autotransfomer; this is the common practice with so called buck-boost transformers.

    The huge benefit of using an autotransformer configuration is that only part of the power goes through the transformer, so you don't need the full kVA rating.

    For 3 phase use, you could use 2 or 3 single phase transformers, connected as autotransformers.

    For your application, I think you could use a set of 3 480V to 120V 10 kVA transformers to boost 480V to 600V with a net capacity in excess of 75 kVA (you only need 5kVA 277 to 70V transformers, but 480 to 120 is a standard rating and likely cheaper). You would need to have an engineer or the transformer supplier do a detailed design.

    -Jon

  8. #8
    Join Date
    Nov 2007
    Posts
    781
    Quote Originally Posted by winnie View Post
    . . . . . . . . . . . . . . . . . . .

    For your application, I think you could use a set of 3 480V to 120V 10 kVA transformers to boost 480V to 600V with a net capacity in excess of 75 kVA (you only need 5kVA 277 to 70V transformers, but 480 to 120 is a standard rating and likely cheaper). You would need to have an engineer or the transformer supplier do a detailed design.

    -Jon
    3 X 10kVA transformers to be connected into 480/600V autotransformer? 480V single-phase transformers connected in wye will be underfluxed when supplied with 480V line-to-line voltage!(supply voltage will be 277V).

    You could use 480/120V single-phase transformers if you wired it open-delta. You only need two-10kVA, 480/120V transformers! Max amps = 83A @ 600V (86.6 kVA)

  9. #9
    Join Date
    Dec 2016
    Location
    pittsburgh, pa
    Posts
    50
    Quote Originally Posted by winnie View Post
    An 'autotranformer' is one where there is a single coil (note: single for a phase) with multiple taps for your input and output voltages, rather than separate primary and secondary coils.

    A single phase transformer with separate primary and secondary coils can be connected as an autotransfomer; this is the common practice with so called buck-boost transformers.

    The huge benefit of using an autotransformer configuration is that only part of the power goes through the transformer, so you don't need the full kVA rating.

    For 3 phase use, you could use 2 or 3 single phase transformers, connected as autotransformers.

    For your application, I think you could use a set of 3 480V to 120V 10 kVA transformers to boost 480V to 600V with a net capacity in excess of 75 kVA (you only need 5kVA 277 to 70V transformers, but 480 to 120 is a standard rating and likely cheaper). You would need to have an engineer or the transformer supplier do a detailed design.

    -Jon
    i am going to look into this. i am not familiar with buck-boost transformers either. this sounds like a good solution as well.

    wouldn't a 480V to 120V be a different ratio than 600V to 480V?

  10. #10
    Join Date
    Dec 2016
    Location
    pittsburgh, pa
    Posts
    50
    Quote Originally Posted by mike_kilroy View Post
    1) "just a single core thng" is a pretty bad description. Most transformers have a "single core" for each phase so that is no unique description for autoxfmr... multiple taps is good sttatement though. Yes, each phase is wound around single core just like an isolation 9iso) xfmr. And just like a typical iso xfmr primary winding, it has "multiple taps." The auto xfmr just stops there: it does not have a secondary winding. Finished. Done. That's all folks. Just a primary winding. So yes, a single winding [per phase] with taps. In your case at 480v and at 600v. Looks just like an iso xfmr. Reason it is cheaper it is just the pri winding, no cost for a secondary winding, and its physical size is reduce to (1-480/600)*75= 15kva physical size; hence you are paying for basically a 15kva xfmr instead of a 75kva.

    2) pros and cons? sure some potential ones already mentioned by other replies. But none of these re likely to effect you at all. Consider: your 75kva xfmr probably has Z (impedance) of about 5%. An auto xfmr has much lower Z than an equi iso, so you may be adding 2% more with it in series. Unless your machine uses some unique requirement servos such as Siemens, that require <3% Z input, this added 2% certainly won't bother it. Especially for just a single test. Sure it is a Y configuration, but like an induction motor, whether it is Y or D config, it has no meaning to you - it is simply going to be used as a voltage change device. Either will do the job as well and as transparently to you and your machine.

    3) No ground required or used; sure you can ground the metal "core" - there is likely a ground terminal on it for you.

    4) Suggest you ask them what they have in stock that can do your job; often they have something. As xfmr supplier, we often can get something required if needed quick so you should be able to - if you ask.

    5) Both places I posted ship worldwide. Many many others do too.

    1) this is the one i am currently looking at. Hammond Power # Y075QTC https://www.hammondpowersolutions.co...otransformers/

    2) i looked quickly thru the spec sheet that this Transformer will be powering, didn't see anything specifying this http://www.signaltestinc.com/v/vspfi..._Datasheet.pdf

    4) so far this morning, I've reached out to Eaton (they wont talk about expediting until they have a P.O.) and waiting to hear back from Hammond Power, hopefully they have something available

    5) I am going to look into these and get quotes from them as well!