Page 1 of 2 12 LastLast
Results 1 to 10 of 11
Thread: Light installation question - fluor. fixture on drywall ceiling
  1. #1
    Join Date
    Mar 2010
    Posts
    242
    Say a 4 foot fluorescent fixture on a drywall ceiling:
    Is a box in the ceiling required? (if yes - what NEC reference?)
    Or can NM wiring be connected directly to the fixture?
    What do you (opinion) think would have been done in the 70s in a low cost multifamily? (4 ft kitchen fixture)
    (An odd question I know, but applies to fixture replacement where the ceiling potentially has asbestos) (I could go look but the apartments in question are over an hour away)
  2. #2
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,156
    No box needed.
    I will look up code section in a minute.
    "Electricity is really just organized lightning." George Carlin
    Derek
  3. #3
    Join Date
    Jan 2009
    Posts
    14,156
    300.15(B)
    (B) Equipment. An integral junction box or wiring compartment
    as part of approved equipment shall be permitted
    in lieu of a box.
    Derek
  4. #4
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    1,164
    Quote Originally Posted by jumper View Post
    300.15(B)
    in lieu of a box.
    This assumes the fixture has such an integral box. Most do, however I have installed fluorescent fixtures that did not and required an external box. Usually the very cheap ones.
  5. #5
    Join Date
    Jan 2009
    Posts
    14,156
    Quote Originally Posted by Coppersmith View Post
    Actually I assume no box, integral or not, cable/wire is just attached with a connector and spliced internally to the ballast.
    Derek
  6. #6
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,383
    I agree, that would be considered the aforementioned wiring compartment.
    Rob
  7. #7
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    4,617
    I would assume no box. If there is one present, it has to be accessible w/o taking down the fixture.
    You have another potential problem: most new fixtures require connection to 90*C wire. Doubt that 40+ year old NM is rated for it.
    What part do you think will be asbestos?
  8. #8
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    4,617
    PS: Asbestos is not like a Black Mamba, instantaneous and deadly. A respirator that filters anything will work on Asbestos. Here, there's a metric ton of it as siding, so long as you dont drill or grind it, you can remove it, and throw it away, w/o even a permit (pipe insulation is a TOTALLY different animal). You're not going to get Mesothelioma from cutting one hole in a ceiling, or disturbing its insulation.
  9. #9
    Join Date
    Apr 2009
    Clarkesville, Georgia
    Posts
    2,039
    Quote Originally Posted by olc View Post
    apartments
    Am curious, how many units?
    Dave Ruth
    Ready Electric
  10. #10
    Join Date
    Mar 2010
    Posts
    242
    Quote Originally Posted by readydave8 View Post
    50ish
Posting Permissions
  • You may not post replies
  • You may not edit your posts