210.12 (A) AFCI protection

Status
Not open for further replies.

JDB3

Senior Member
All circuits supplying outlets or devices in the kitchen shall be AFCI protected.
I know what this says, but, does this mean, that the { }stove hood, { } built in microwave shall be AFCI protected? Just mainly want clarification from others on this, so I may inform contractor the opinion of others on this. This in an area that does not get inspections, so therefore there is not an AHJ to ask their opion on this.
Thanks,
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
IMO, this says it all. To answer your question- yes everything min the kitchen that is fed with 120-V 15 or 20 amp circuit

210.12(A) Dwelling Units. All 120-volt, single-phase, 15- and
20-ampere branch circuits supplying outlets or devices installed
in dwelling unit kitchens, family rooms, dining
rooms, living rooms, parlors, libraries, dens, bedrooms,
sunrooms, recreation rooms, closets, hallways, laundry areas,
or similar rooms or areas shall be protected by any of
the means described in 210.12(A)(1) through (6):
 

JDB3

Senior Member
Thanks Dennis.
Only the receptacles serving the kitchen counter top or within 6 feet of the sink, shall be GFCI protected
( ) True ( ) False ( ) Exceptions _________________________________
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Thanks Dennis.
Only the receptacles serving the kitchen counter top or within 6 feet of the sink, shall be GFCI protected
( ) True ( ) False ( ) Exceptions _________________________________

All counter receptacles in the kitchen that serve the countertops must be gfci protected
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Thanks Dennis.
Only the receptacles serving the kitchen counter top or within 6 feet of the sink, shall be GFCI protected
( ) True ( ) False ( ) Exceptions _________________________________
Because your first reference to the AFCI requirements only exists in the 2014 NEC, it follows that this question is to be answered from the same edition of the Code.

Your GFI question is not easily answered as written. First, as Dennis says, ALL kitchen countertop receptacle outlets must have GFCI protection. . . BUT, it doesn't stop there. New in the 2014, is the "six foot" requirement from sink edge, expanded to ANY dwelling unit sink, and it is written such that the receptacle behind an appliance or the receptacle on the other side of a peninsula gets GFI if within the six foot (210.8(A)(7)).

Also new in the 2014, the dishwasher in a dwelling gets GFCI whether it is cord and plug connected or hardwired, regardless of location. (210.8(D))
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Thanks,
Nice to what we are in for in a couple of years.
Looks like full space , large number of breaker panels.
 