    Does the 2017 NEC permit 110 voltage AC and 277 voltage AC in the same conduit if they are originated in the same lighting control panel where the 277 volt lighting circuitry is also stepped down to 110 for receptacles of the same lighting area serviced?
    All conductors in the same conduit are originated from the same Source lighting control panel and are insulated at 600 volts ac.
    All conductors are appropriately fused with circuit protection in the lighting control panel.
  2. #2
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,613
    Yes. I don't have time right now to look up the relevant article. But as long as all conductors have an insulation system that is rated for the highest voltage in the conduit, you are allowed to mix voltages in the conduit. For your example, the conductors will all have a rating of 600 volts.
    Welcome to the forum.
    Charles E. Beck, P.E., Seattle
    Comments based on 2014 NEC unless otherwise noted.
  3. #3
    Join Date
    Jul 2003
    New Jersey
    Posts
    23,424
    You also would need to identify the neutral of each system. Typically one method is by using white for 120 volts and gray for 277. If the building has both systems then the voltage would likely be 208Y/120 so it's 120 volts not 110.
    Rob
  4. #4
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,484
    300.3(C), 200.6(D) for those keeping score at home.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    32,923
    Quote Originally Posted by infinity View Post
    Ungrounded conductors of each system need identification as well.
  6. #6
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    4,186
    480Y/277V and 208Y/120V cannot be in the same panel. Raceways from each could go to a common j-box, then out from there to the loads served, so long as they comply with the aforementioned code sections.
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    32,923
    Quote Originally Posted by JFletcher View Post
    You sure about that?
    Remember a panelboard gets installed in a cabinet, so you are not so likely to land both systems on the same panelboard, but they can be in the same cabinet.
    There are "mini power zone" assemblies that have 480 volt primary breaker, transformer and 120/208-240 secondary panelboard all in one enclosure.
  8. #8
    Join Date
    Jul 2003
    New Jersey
    Posts
    23,424
    Quote Originally Posted by kwired View Post
    Yes they can occupy the same panel you would just need to identify the conductors that are passing through.