Hello,

Can anyone tell me where the code specifies FMC to a transformer for vibration mitigation? Or is that just common practice? :)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
IMO it's more of a common practice than a code requirement unless the transformer is on springs, isolators or some sort of other mechanical device that would allow it to move.
 
I dint believe it is in the code, however installation must be to manufacturers specification. It may be in the installation Manual. I know I read it somewhere before but it may have just been a recommendation.
 

rlundsrud

Senior Member
Location
chicago, il, USA
I agree with Iwire, there has never been a code that required it, it was always just a common practice. The only exception would be if the manufacturer specs it then it must be installed as such. I have never seen an installation that wasn't FMC, but I suppose there is one out there somewhere.
 