    Fire alarm

    When you relocate pull station from 64" to 48" AFF to comply with ADA, can you slice wiring?

  2. #2
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    12,035
    Yes, but there are rules to follow.

    See 760.53(A)(1) and 760.130(B)(1). Check local amendments.

    Some specs do allow splices except at device boxes and terminal cabinets.
    "Electricity is really just organized lightning." George Carlin


    Derek