Results 1 to 6 of 6
Thread: Arc Flash calculations
  1. #1
    Join Date
    Aug 2014
    Tempe, AZ
    Posts
    25
    Hello All,
    I am performing arc flash analysis on small MV system, 12.47kV is the service voltage with some 12.47 equipment and goes down to 208V. I have couple of questions on the calculations:
    1. For arc flash, IEEE 1584 equations are used which are typically for 3-phase faults. Why is line-ground fault not considered for arc flash? Is the reason that line-ground fault quickly turns into a three phase fault in 15kV or small systems?
    2. Now the code requires to install a arc flash mitigation system for systems rated for 1200A or more. These arc flash mitigation is typically designed for a 3-phase arcing fault. For example a maintenance setting is provided for a 3-pole 2000A breaker. The maintenance setting reduces the instantaneous to 5000A to lower the arc flash energy, but the ground fault is set for a instantaneous of 2000A, which is still lower than the maintenance setting. Why is still the L-G not considered for arc flash?
  2. #2
    Join Date
    Mar 2013
    Rutland, VT, USA
    Posts
    303
    Basically the premise in IEEE 1584-2002 is that a fault that would cause an arc flash is a 3 phase one and all the testing done to develop the equations were 3 phase. They consider that an arcing fault is started by a L-G fault would rapidly progress to a 3 phase fault. There are no equations to do a single phase arc fault so there are two ways to handle that: calculate it as a 3 phase knowing that the result will be conservative or state that it is exempt from analysis and give it a default incident energy level.
    Is this your first time doing an arc flash analysis? If so are working under the guidance of an engineer experienced in arc flash studies?
  3. #3
    Join Date
    Jun 2017
    WI, USA
    Posts
    313
    Quote Originally Posted by wbdvt View Post
    Concur.
  4. #4
    Join Date
    Aug 2014
    Tempe, AZ
    Posts
    25
    Thank you.
    This is not my first one and yes it is performed under the guidance of experienced PE. I got this question since on open switchyard typically line - ground fault is fused for arc flash calculation. i assume the reason being the distance between buses larger in open switchyard compared to lower voltage systems. This is only reason I was prompted to ask the question if my understanding of not performing the single-line to ground arc flash on less than 15kV systems, was not correct.
  5. #5
    Join Date
    Mar 2013
    Rutland, VT, USA
    Posts
    303
    If it is a switchyard or substation you may be in realm of OSHA 1910.269 for utility or utility like equipment where arc flash is specifically mentioned. In Appendix E there is a table of recommended methods to calculate incident energy. One of them for single phase <15kV is using Arc Pro and IEEE 1584 for 3 phase. Above 15kV the table has Arc Pro
  6. #6
    Join Date
    Jan 2018
    Midland, TX, USA
    Posts
    5
    Phase to ground Fault
    FYI, stats show that most (70%-80%) may begin as phase to ground faults but then, due to the expansive nature of conductive metals and electricity, very quickly progress to 3 phase faults.
    Im with wbdvt on this one.
    "Resistance is not futile....its voltage divided by current."
Tags for this Thread
Posting Permissions
  • You may not post replies
  • You may not edit your posts