    60 C termination.

    If I have a buss switch that has 60c rated connection point, for a 50 amp fuse, is it feasible to use # 6 THHN to that then go to a junction box and connect #8 type W cord for a drop?

  2. #2
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    11,954
    Quote Originally Posted by Deetz View Post
    If I have a buss switch that has 60c rated connection point, for a 50 amp fuse, is it feasible to use # 6 THHN to that then go to a junction box and connect #8 type W cord for a drop?
    W is listed as extra hard usage for 368.56(B) and Table 400.5(A)(2) says either 55A or 48A depending if it's 2 wire or 3 wire, so assuming load does not exceed values, it seems okay.
    "Electricity is really just organized lightning." George Carlin


    Derek

  3. #3
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,347
    Quote Originally Posted by Deetz View Post
    If I have a buss switch that has 60c rated connection point, for a 50 amp fuse, is it feasible to use # 6 THHN to that then go to a junction box and connect #8 type W cord for a drop?

    Yes that can be done and in fact, is a great way to solve issues with large wires on long runs.