Page 1 of 2 12 LastLast
Results 1 to 10 of 11
Thread: Breaker size for Chevy Volt
  1. #1
    Join Date
    Apr 2008
    Logan, Ut
    Posts
    23
    I just bought a Chevy Volt and I want to install a 240 V charger. The Volt charging system is limited to 3.6 KW max. I have s spare 30A 240 V breaker in the panel. I got a deal on a charger that is rated for 30A. This is overkill for the 15A load that I need. The installation instructions call for a 40 A breaker. Does the code call for a 40A or do I size for the cars load. I really don't want to use a larger breaker than I need. This is on a dedicated circuit that is hardwired to the charging station.
    Thanks
  2. #2
    Join Date
    Feb 2007
    USA
    Posts
    5,544
    If the charge station requires a 40 a then you would need a 40a circuit.
  3. #3
    Join Date
    Apr 2008
    Logan, Ut
    Posts
    23
    Quote Originally Posted by Sierrasparky View Post
    Where in the code is this called for?
  4. #4
    Join Date
    Feb 2007
    USA
    Posts
    5,544
    Quote Originally Posted by dnyman View Post
    I don't recall the code section but it has to do with manufactures requirements.
  5. #5
    Join Date
    Nov 2013
    New England
    Posts
    321
    My $0.02- seems OK to wire it for 30A knowing you can't use the charger to its max capacity. There is a chance there is still an inrush on the charger that could trip a 30A breaker. Only the manufacturer will know, and they probably won't say anything under 40A will work. No safety issue so I don't think NEC will care. Like wiring a 1HP motor to a 20A circuit. It's allowed by NEC but you may trip the breaker.
  6. #6
    Join Date
    Feb 2007
    USA
    Posts
    5,544
    ok I found it.
    By code you must install to manufactures requirement ... So if the instructions or listings say "requires 40 or 50 amp "
    then you must do so.
    110.3 b
    (B) Installation and Use.
    Listed or labeled equipment shall be
    installed and used in accordance with any instructions included
    in the listing or labeling.
  7. #7
    Join Date
    Apr 2008
    Logan, Ut
    Posts
    23
    SierraSparky,
    Thanks for the reply.
  8. #8
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,244
    Thanks
    How EXACTLY do the instructions read?
    "Requires individual branch circuit with 40A OCPD"
    "Recommend a 40A breaker"
    110.3(B) requires you to follow mfg instructions. That written, mfg instructions can be somewhat vague or use incorrect terminology, like the word "dedicated".
    If the instructions require a 40A breaker, then you should use a 40A. Using a 30A would be an NEC violation, that if I had to rate on a scale of 1-10, 1 being a technical violation and 10 being "your house will burn down any second", using a 30A here in place of a 40A is a zero. Nuisance trips are the only potential problem here.
  9. #9
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,549
    This is one of those situations. If it doesn't work, do it over.
    If you have to run new conductors anyway, why is a $15 CB a problem?
    Tom
    TBLO
  10. #10
    Join Date
    Jul 2005
    LA basin, CA
    Posts
    1,745
    ..The Volt charging system is limited to 3.6 KW max. I have s spare 30A 240 V breaker in the panel. I got a deal on a charger that is rated for 30A. This is overkill for the 15A load that I need.
    If charger operates at 3.6kw/120vac then load ampacity is 30A x 1.25 for continuous loads = 37.5A --> 40A Breaker
    Further, doing 30A continuous with #10cu Romex operates near 64'C, overheating the MAX 60'C listing of NM cable conductors & some fuse-box equipment.
    The only way ampacity is closer to 15A, is if your charger operates at 240vac, requiring use of both hot legs, not just one.
    Roger Ramjet NoFixNoPay
Posting Permissions
  • You may not post replies
  • You may not edit your posts