    found a three pole 480/277 breaker today. Only being used for one pole lighting circuit. Is this Ok ?
  2. #2
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,240
    Quote Originally Posted by wireday View Post
    Wasteful, but not any kind of code violation AFAIK.
  3. #3
    Join Date
    Oct 2009
    Posts
    198
    I think it was an available unused breaker, and they added a lighting circuit.
  4. #4
    Join Date
    Jan 2011
    United States
    Posts
    7,289
    100% ok.
    I'm in over my head...
  5. #5
    Join Date
    Jul 2006
    San Francisco Bay Area, CA, USA
    Posts
    7,734
    100% OK, but only IF you have a 480/277V system. We can assume you do because you must be using a neutral, but it's worth mentioning because we cannot see your system.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  6. #6
    Join Date
    Oct 2009
    Posts
    198
    Yes its a 277 with neutral for lighting circuit.
  7. #7
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    Quote Originally Posted by GoldDigger View Post
    I agree. Are you saying wasteful tho from the standpoint of using a 3p breaker when a single would suffice, or wasteful by using 277V when 480V, if the fixtures have xfmrs with taps for it, would be much more efficient?
    Electricians do it until it Hertz!
  8. #8
    Join Date
    Dec 2012
    Posts
    19,240
    Quote Originally Posted by JFletcher View Post
    Just the breaker.
    Sent from my XT1585 using Tapatalk
  9. #9
    Join Date
    May 2014
    AZ
    Posts
    2,321
    does the AHJ require you to label what is in-use and what is spare? are the unused poles of a ocpd considered "spare"?
    thats the only other thing i can think of.