    Determining motor ampacity for motors greater than 500 Horespower

    Hey all,

    The tables specified in section 430.6 to determine motor ampacity only go to 500 horsepower (T430.250 in my case). If have a 657 HP motor I assume I use the data plate amperage? I can't find anything in the book that addresses this.
    *Sometimes I wonder why the frisbee keeps getting bigger...and then it hits me!

  2. #2
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    8,657
    Quote Originally Posted by Electron_Sam78 View Post
    Hey all,

    The tables specified in section 430.6 to determine motor ampacity only go to 500 horsepower (T430.250 in my case). If have a 657 HP motor I assume I use the data plate amperage? I can't find anything in the book that addresses this.
    The data nameplate says 657 HP?
    Tom
    TBLO

  3. #3
    Join Date
    Aug 2007
    Location
    Palm Bay, FL
    Posts
    655
    That's what I'm told. I've been asked to size a disconnect for it.
    *Sometimes I wonder why the frisbee keeps getting bigger...and then it hits me!

  4. #4
    Join Date
    Aug 2007
    Location
    Palm Bay, FL
    Posts
    655
    480 volts, 790 amps, 70 Hz, 2088 RPM
    *Sometimes I wonder why the frisbee keeps getting bigger...and then it hits me!

  5. #5
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    17,901
    Quote Originally Posted by Electron_Sam78 View Post
    480 volts, 790 amps, 70 Hz, 2088 RPM

    70 Hz? I guess not a typo since it matches 2088 RPM. Requires a VFD? Or powered by dedicated generator?

  6. #6
    Join Date
    Aug 2007
    Location
    Palm Bay, FL
    Posts
    655
    Running by VFD
    *Sometimes I wonder why the frisbee keeps getting bigger...and then it hits me!

  7. #7
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    32,898
    Quote Originally Posted by Electron_Sam78 View Post
    Running by VFD
    That there tells you to look at the drive requirements, at least for the supply circuit. Output I would say size conductors for nameplate amps (x 125%).

  8. #8
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    8,657
    I would think the drive has some sort of recommendation for protection on the line side of it.
    Tom
    TBLO

  9. #9
    Join Date
    Aug 2007
    Location
    Palm Bay, FL
    Posts
    655
    So if this disconnect needed to be between the VFD and the motor am I to understand the NEC doesn't have guidance for this as far as determing motor ampacity? So revert to data plate ratings?
    *Sometimes I wonder why the frisbee keeps getting bigger...and then it hits me!