    It seems to me, the Grounding Electrode Conductor (GEC) should be unspliced from the transformer XO to the nearest grounding electrode. However I cant find where the NEC actually states this. Am I missing something?
  2. #2
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,363
    In general the GEC can only be irreversibly spliced. It can terminate on a common terminal with a bonding jumper to the X0.
    Rob
    All responses based on the 2014 NEC unless otherwise noted
  3. #3
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,565
    250.64(C).
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.
  4. #4
    Join Date
    Apr 2016
    Georgia
    Posts
    494
    Quote Originally Posted by ActionDave View Post
    250.64(C).
    Thanks to All