Thread: Mandatory backup power for HVAC systems in Heath Care Facilities

  1. #11
    Join Date
    Jan 2011
    Location
    United States
    Posts
    6,654
    Quote Originally Posted by don_resqcapt19 View Post
    My understanding is that the NEC only provides the installation requirements, and NFPA 99 specifies what is to be backed up. In 517, the requirements that tell what is to be backed up all have a [bracketed] reference to NFPA 99. That means the information preceding the brackets has been extracted from 99.
    Makes sense. So in order to change the NEC, I'd need to change 99, right?
    What is esoteric knowledge today will be common knowledge tomorrow.

  2. #12
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,287
    Quote Originally Posted by mbrooke View Post
    Makes sense. So in order to change the NEC, I'd need to change 99, right?
    Probably no need to do anything with the NEC. Just a requirement that in 99 that those facilities have AC systems supplied by a back up power system.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)

  3. #13
    Join Date
    Sep 2017
    Location
    Claverack, NY, USA
    Posts
    15
    This type of requirement, if proposed should be in the building code, not the NEC