Page 1 of 2 12 LastLast
Results 1 to 10 of 13
Thread: Mandatory backup power for HVAC systems in Heath Care Facilities
  1. #1
    Join Date
    Jan 2011
    United States
    Posts
    7,716
    Would mandating cooling systems to be (required) on backup power in health care facilities and nursing homes be a worthwhile code proposal? While we do not know the specifics in this case, over the years I have seen many stories where facilities loose power and quickly become functionally inoperative due to the lack of AC.
    https://www.nytimes.com/2017/09/13/u...a.html?mcubz=0
    Many major hospitals and level 1 trauma centers have moved to full backup power finding it pays for itself, but currently it is not required by code.
    I'm in over my head...
  2. #2
    Join Date
    Aug 2006
    Miami Fla.
    Posts
    7,459
    Nursing homes here in Fl are required to have an "alternative source of power" although there is no requirement as to what that shall be.
  3. #3
    Join Date
    Jan 2011
    United States
    Posts
    7,716
    Quote Originally Posted by chris kennedy View Post
    Does it mention how much it should power?
  4. #4
    Join Date
    Aug 2006
    Miami Fla.
    Posts
    7,459
    Not sure, heard it on NPR this morning. We take care of a number that have Genny's for life safety and critical but not HVAC.
  5. #5
    Join Date
    Jan 2011
    United States
    Posts
    7,716
    Thats usually how it is, only the bare minimum is put on generator as code requires.
  6. #6
    Join Date
    Feb 2003
    Illinois
    Posts
    23,652
    I expect that proposal would have to be to NFPA 99, and not NFPA 70. 99 is the controlling document for health care facilities.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  7. #7
    Join Date
    Jan 2011
    United States
    Posts
    7,716
    Quote Originally Posted by don_resqcapt19 View Post
    But 70 holds the requirements for what is to be backed up and to which branch/ATS. I mean the two go hand in hand, at least thats my understanding.
  8. #8
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    7,912
    Yes 99 and 70 do go hand in hand. We are past the cutoff for first drafts for the 2020 NEC, if the NFPA 99 revision cycle starts in the next three years start there. Otherwise you will be on the 2023 NEC
    Moderator-Washington State
    Ancora Imparo
  9. #9
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,546
    Quote Originally Posted by mbrooke View Post
    The way I see it is if 99 would call an HVAC load a critical load then 70 would have to treat it as one. I could see this being more likely for surgical areas, critical care areas, etc. but more likely an optional load if to be transferred for general care areas.
  10. #10
    Join Date
    Feb 2003
    Illinois
    Posts
    23,652
    My understanding is that the NEC only provides the installation requirements, and NFPA 99 specifies what is to be backed up. In 517, the requirements that tell what is to be backed up all have a [bracketed] reference to NFPA 99. That means the information preceding the brackets has been extracted from 99.