    energized water
    Is there any device or measuring instrament that can detect if there is electrical presence in a body of water. In light of hurrican damage in texas and florida. Similar to a non contact tester that all us electricians have. Just wondering
  2. #2
    Join Date
    Mar 2010
    Lake of the Ozarks
    Posts
    1,034
    Quote Originally Posted by forcebjj View Post
    Never used it and I would not bet my life on it but there is this
    http://www.homedepot.com/p/Shock-Ale...2500/301698076
    1N73LL1G3NC3 15 7H3 4BILI7Y 70 4D4P7 70 CH4NG3.
  3. #3
    Join Date
    Dec 2016
    Chicago Illinois
    Posts
    7
    good find! never used it either but maybe better than nothing
  4. #4
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,211
    Just putting a high impedance voltmeter probe on a stick and dangling the other probe into the water next to your legs will give a pretty good indication of energized water in your vicinity. But watch out for vertical gradients in the water potential when an exposed conductor is running on the earth below more than just a couple of inches of water.
  5. #5
    Join Date
    Feb 2013
    India
    Posts
    2,456
    Also there may be dangerous ground potential gradient along any moist surface adjacent to energized body of water so that current may enter the body through two legs while trying to throw the device into the water body to check voltage!