Results 1 to 9 of 9
Thread: BREAKER REQUIREMENT FOR GENERATOR TRANSFER SWITCH
  1. #1
    Join Date
    Feb 2010
    Posts
    10
    Hi, I have a generator installation 350 KW 120/208. The AHJ says I need to add a stand alone 200 amp breaker, in the transfer switch, to protect the conductors between the generator (600 amp breaker) and the transfer switch. My thought is the 200 amp main in the service panel would protect those conductors from overloading. I'm looking at it like primary or secondary protection on a transformer. Normally I would just put it in and move on but I have a 400 amp transfer going on the same generator. Any help would be appreciated. Pat.
  2. #2
    Join Date
    Dec 2010
    Posts
    1,389
    What size are the conductors, and what do they run between? More detail please.
    The more they overthink the plumbing, the easier it is to stop up the drain
  3. #3
    Join Date
    Feb 2010
    Posts
    10
    Quote Originally Posted by pat04607 View Post
    Not sure on the aerial run, that was done by a line co. The aerial goes to a mast on the transfer switch with 3/0 cu for the phase conductors.
  4. #4
    Join Date
    Jun 2015
    nyc
    Posts
    127
    It's hard to visualize the situation from description. Sketch will help.
    Sent from my Nexus 5X using Tapatalk
  5. #5
    Join Date
    Feb 2010
    Posts
    10
    Hi, Rather than over think details my question is this, If the conductors are rated for 200 amps then why wouldn't the 200 amp main in the panel protect them from overload? Why would you need a 200 amp breaker in the transfer switch?
  6. #6
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,578
    Because you have a 600A semi truck ready to crush a 200A mo ped if the brakes fail.
    I'm not understanding the inspectors idea of adding another 200A breaker at the transfer switch either. The AIC wouldn't be enough would it? You need another breaker at the generator.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.
  7. #7
    Join Date
    Jun 2003
    Posts
    6,893
    You generally have to protect conductors at their source, not the load end. So a 200A breaker at the panel wouldn't protect the wiring from the generator to the panel, and the 600A breaker won't protect the wires unless they are rated for the full 600A. There are some tap rule exceptions, and some specific exceptions for transformers also.
    Also, I'm not sure its a definite rule, but I always protect a 200A ATS with no more than a 200 amp OCP in front of the ATS.
  8. #8
    Join Date
    Mar 2013
    Rutland, VT, USA
    Posts
    321
    The generator breaker may be a 600A frame but have a much smaller rating plug anywhere from 200A to 600A so need more detail on the breaker, trip unit and conductors from the generator to transfer switch.
  9. #9
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,640
    If I understand the OP correctly, he has a 200 amp ATS and it's feeder conductors protected by a 600 amp upstream OCPS. The issue would not be just that the conductors are not properly but also the ATS is not protected per the NEC and UL standards. UL standards have very specific requirements for OCPDs for ATSs. The type and size will depend on things such as available fault current.
Posting Permissions