    data and fire alarm cable in same bridle rings

    Ive looked and cannot find this question. Can i run data and fire alarm cable in the same bridle rings?

  2. #2
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    4,564
    Quote Originally Posted by hunterhartter View Post
    Ive looked and cannot find this question. Can i run data and fire alarm cable in the same bridle rings?
    Yes, as long as:

    1. The fire alarm cable is power limited (Class 2 or Class 3 source)
    2. There is no local amendment prohibiting this (check with the AHJ/building departemnt)
    3. There is no restriction in the specifications or on the drawings regarding co-location of these cable types.