Page 2 of 8 FirstFirst 1234 ... LastLast
Results 11 to 20 of 80
Thread: zig zag transformer
  1. #11
    Join Date
    Mar 2008
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    9,912
    Quote Originally Posted by kwired View Post
    There is no neutral conductor running to it on the drawing though, just indicates a ground connection at the midpoint.
    To me, it looks like the midpoint is the artificial neutral, and the only purpose of it is to provide a balanced connection to the earth.
    Cheers and Stay Safe,
    Marky the Sparky
  2. #12
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    37,098
    Quote Originally Posted by K8MHZ View Post
    Yet the source ahead of this appears to already be a grounded wye, which should already fulfill that purpose.
  3. #13
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,285
    Looking hard at the drawing, I renew my comment that the source grounding is only seen when the disconnect is closed, since there is no neutral connection to the inverters. I do not see why floating the inverter output (when not operating, because of anti-islanding) should be harmful, but it still might be the motivation.
  4. #14
    Join Date
    May 2011
    Posts
    4,258
    Quote Originally Posted by GoldDigger View Post
    While it's a little hard to say for sure with the photo cutting things off, it does look to me like the neutral goes to the inverters. It seems like the drafter just omitted the neutrals inside the switchboard for clarity.
    Not saying you are wrong about the motivation, we've heard about demands for source grounding (which to my knowledge is unnecessary). I also wonder what you think of my 705.32 comment though.
  5. #15
    Join Date
    Dec 2011
    Ocala, Florida, USA
    Posts
    2,586
    Also notice the cutting off. It looks like the breaker is a normally open breaker that closes upon activation of the "S" on the right side of the page. Perhaps seeing the rest of the drawing would give some clue as to the intention. I don find it interesting that this is odd enough that no one here with the vast knowledge represented, has yet said, "Oh that is a ..."
    I know what I don't know, and I know where to go to find it!
  6. #16
    Join Date
    Jan 2016
    PA
    Posts
    5,697
    It is a grounding xfmr for the 480
    the assoc cb looks like it is tripped by a 0 seq on the 13.2 kv prim?
    why I do not know
    it does gnd the load side of the 3000 fused sw if open
    The difference between genius and stupidity is that genius has its limits.
  7. #17
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    4,391
    Quote Originally Posted by Strathead View Post
    Here is a more complete picture. I am confused by the logic of the kirk key. Here is what the note 11 says:
    "Direct trip. If 480V 1200A circuit breaker is open, trip sent to 13.2KV 1200A VCB."
    So if the Zig Zag or its supply circuit fails, in such a way that causes the breaker to trip (or someone manually turns it off for that matter), they want the MV supply to also open. The 480 system is already grounded, so why is the zig zag needed, and not only that, why do they see it as so important that the MV supply opens if the zig zag goes offline? Is this just perhaps a silly utility requirement based on grounding myths that system grounding is of paramount importance and that "more" is better?
    Attached Images Attached Images
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  8. #18
    Join Date
    Jun 2004
    Posts
    4,391
    The inverters are SMA sunny tripower, 30KW and do have a neutral. But I do agree that the motivation is likely to do with some (irrational) fear that the inverters will lose their reference to ground and float. Not only do I see that is very imnprobably, but even if it did I dont see that as that big a deal really.
  9. #19
    Join Date
    Jul 2006
    Roughly 5346 miles from Earls Court
    Posts
    2,601
    Quote Originally Posted by electrofelon View Post
    1200A at 13.2KV ??? That can't be right.
    (Is this when an RFI becomes a WTF?)
  10. #20
    Join Date
    Mar 2013
    Rutland, VT, USA
    Posts
    321
    Quote Originally Posted by zbang View Post
    Why? A 25MVA, 13.2kV Transformer would be about 1100A full load. The system is being supplied by National Grid and this may be a large manufacturing facility supplied off of a 115kV transmission line.
Posting Permissions
  • You may not post replies
  • You may not edit your posts