    zig zag transformer

    What is the purpose of the ziz zag transformer in this drawing?
    Attached Images Attached Images  
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  2. #2
    Join Date
    Jul 2005
    Location
    LA basin, CA
    Posts
    1,610
    Quote Originally Posted by electrofelon View Post
    What is the purpose of the ziz zag transformer in this drawing?
    Used to create artificial neutral, mitigate harmonics, & more. Check it out on Wikipedia:
    https://en.wikipedia.org/wiki/Zigzag_transformer
    Roger Ramjet NoFixNoPay

  3. #3
    Join Date
    Jul 2006
    Posts
    2,441
    Looks like it's being fed from a grounded wye secondary, so that's a good question.

  4. #4
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    18,445
    The customer transformer is a grounded wye-grounded wye transformer, so I do not see any need for a grounding transformer.
    The only thing I can think of is that someone has specified that the inverter output has to remain solidly grounded even when the disconnect is open.

  5. #5
    Join Date
    May 2011
    Posts
    3,805
    I really know nothing, except that I can tell this has something to do with it.
    Attached Images Attached Images  

  6. #6
    Join Date
    May 2011
    Posts
    3,805
    Quote Originally Posted by GoldDigger View Post
    The customer transformer is a grounded wye-grounded wye transformer, so I do not see any need for a grounding transformer.
    The only thing I can think of is that someone has specified that the inverter output has to remain solidly grounded even when the disconnect is open.
    I can't see how an open disconnect would unground the inverter output.

  7. #7
    Join Date
    May 2011
    Posts
    3,805
    Here's a wild and possibly completely boneheaded guess, since I have no understanding of how/why it would work, but...

    Having noticed this (yellow highlight is mine)...

    Click image for larger version. 

Name:	zig zag gfp.PNG 
Views:	80 
Size:	49.3 KB 
ID:	18611

    ...perhaps it is a way of complying with the exception to 705.32, when using a switchboard that was not designed for backfeed.

  8. #8
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    18,445
    Quote Originally Posted by jaggedben View Post
    I can't see how an open disconnect would unground the inverter output.
    I was thinking (mistakenly) of the disconnect also opening the neutral.
    If there is no neutral connection to the inverters (line to line operation) then opening the three line conductors opens all connections between inverter output and ground.

    Sent from my XT1585 using Tapatalk

  9. #9
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    3,302
    The customer takes service at, and has mv switchgear. Could that have anything to do with it?
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  10. #10
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,690
    Quote Originally Posted by ramsy View Post
    Used to create artificial neutral, mitigate harmonics, & more. Check it out on Wikipedia:
    https://en.wikipedia.org/wiki/Zigzag_transformer
    There is no neutral conductor running to it on the drawing though, just indicates a ground connection at the midpoint.